Fair comment guys , seems this quite a regular occurance.
Yes indeed;
Some managers said just commission the system as you found it, make it working, and test all detectors for normal working operation and so on..., sign a hand over the commissioning certificate and that's it.
Thinking money only
I had been in a situation were an important part of the floor did not have any sounders or bells. even the drawings I had been given did not state any on that area, the drawing was not looking as a professional clean design, it was in fact young electrician who carried out the 1st and 2nd fix as he'd been told just by words of mouth.
Yes such things still exist nowadays
The electrician left for holiday... and left us with many open, short circuit and missing parts…
I made a full report and send it to my manager, as usual he was busy with ......, he could not remember where he saved the report, as a result, after hand over the customer started normally their first weekly bell test it was in fact their first (fire drill), they straight away reported to us that in one of the floors the tenant did not evacuate because none of them had heard alarms.
After investigation and serious meetings with seniors managers of all concerned parts, the blame was to put on us for the simple reason that we had issued a commissioning certificate not stating any thing wrong, the company had paid for all of that extra work to fit extra sounders... as a result I was the first to be blamed because I did not handover a copy of the report with the commissioning certificate to customer.
This last bit was my mistake and hopefully only the once