Author Topic: Node missing in an Advanced Network of 8 panels ????  (Read 16451 times)

Offline Benzerari

  • Hero Member
  • *****
  • Posts: 1391
    • http://benzerari.tripod.com/fas/
Node missing in an Advanced Network of 8 panels ????
« Reply #15 on: November 24, 2007, 01:26:12 PM »
Quote from: Graeme
out of interest i take it 7 floors and the 2nd floor was node 6 then the network cannot have been wired as node 1 to 7 as recommended?

i would have had node 1 ground floor  2 1st floor   3 2nd floor etc..

but for node 6 to be on the 2nd floor would suggest that the wiring does not go from node 1-2 etc and it could be a case that node 6 has never been wired in to the network and it sits last in line and the other panels which are currently programmed as a seven panel network will be nother the wiser as it's  a radial network and not fault tollerant.

the stand alone panel if not wired into the newtwork correctly and programmed to node 8 will be looking for node 9 or 1 which will cause node missing on this panel only and not a network fault globally.
The reason I said 7 floors is to simplify the picture to the readers, in fact there are: basement, ground, and 4 floors with nodes set out as follows:

Ground floor: 3 panels or 3 nodes, one in each entrance, one of them is the main panel 'node 1'
Basement: 1 panel 'node 4'
First floor: 1 panel 'node 5'
Second floor: 1 panel 'node 6'
Third floor: 1 panel 'node 7'
Fourth floor: 1 panel 'node 8'

How ever, Advanced technical support engineer said the networked panel can not reset back to 'node 0' only if some one make some changes manually in the settings through the built on key pad or uploading a different config file different than the original one...

Although, after investigating with my colleagues, who been in that site, as I have been only once. it appears to be that, the site is serviced by a different company on our behalf, we deal with call out issues when required... so one of their engineers may have changed the settings by mistake, and definitely not the tenant... so it seems that there is light at the end of the tunnel soon.

Thanks for all contributors

M C Benzerari

Offline Benzerari

  • Hero Member
  • *****
  • Posts: 1391
    • http://benzerari.tripod.com/fas/
Node missing in an Advanced Network of 8 panels ????
« Reply #16 on: November 24, 2007, 01:56:05 PM »
Although, I think it can not be a hardware sort of faults, because when programmed back the node of the second floor to 'node 6' and carried out a test through one of the call points in that floor, alarm went off normally, intermittent alarm went off in the first and third floor as normal, and our AMX software in switch board room received fire condition as normal with the right input address, time and date...