Author Topic: BS5839 part 1- clause 45.3- recommendations for inspections and tests  (Read 13812 times)

Offline AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2480
    • http://www.firewizard.co.uk
BS5839 part 1- clause 45.3- recommendations for inspections and tests
« Reply #15 on: January 09, 2008, 07:32:57 PM »
Emergency lighting is another area where maintainers overdo it.

Several still do two visits a year conveniently forgetting (or in some cases not knowing themselves) that only an annual duration test is required on top of the monthly flick tests and some do four a year with the fire alarm.

I agree on a lot of fire systems 2 visits is adequate.

Whenever I uncover excess service visits I always find the occupier was going on the companies info as oppose deciding based on a combination of risk/complexity/BS requirements

What's the comparative cost differences between conventional & addressable systems? I sometimes find straightforward simple smaller premises have had an all singing all dancing addressable system put in despite there being little real benefit for the particular area compared to a conventional system
Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36