Author Topic: Haes conventinal panel  (Read 4272 times)

Offline Davro

  • Jr. Member
  • **
  • Posts: 75
Haes conventinal panel
« on: January 30, 2008, 07:26:24 PM »
Does anybody out there know how to put this (HAES PANEL WHICH ONLY HAS FOUR BUTTONS ON IT),into a one man walk test.The panel is approx made in 1998/9.

Offline Benzerari

  • Hero Member
  • *****
  • Posts: 1391
    • http://benzerari.tripod.com/fas/
Haes conventinal panel
« Reply #1 on: January 30, 2008, 07:48:26 PM »
Quote from: Davro
Does anybody out there know how to put this (HAES PANEL WHICH ONLY HAS FOUR BUTTONS ON IT),into a one man walk test.The panel is approx made in 1998/9.
Why not downloading their guides they are free from HAES website? you can find more than what you expect

It is free mate!

Graeme

  • Guest
Haes conventinal panel
« Reply #2 on: January 30, 2008, 08:42:48 PM »
Quote from: Davro
Does anybody out there know how to put this (HAES PANEL WHICH ONLY HAS FOUR BUTTONS ON IT),into a one man walk test.The panel is approx made in 1998/9.
may be the model which has all the engineer functions on the main pcb which you need to take the front cover off to access.

Offline Galeon

  • Hero Member
  • *****
  • Posts: 556
  • Dont ask me on here for advice , come down the Pub
Haes conventinal panel
« Reply #3 on: January 31, 2008, 09:19:10 AM »
You need to make sure the key is in the enable position and the aux relays are shown disabled , then on the rear pcb bottom edge by batteries you will see a a switch marked omt one man test , use that and away you go. If you forget to restore this function , the panel will remind you so there is no chance you can leave it in test.
It will put all zones in test , so unlike some panels if you walk out of a specific zone it comes out of test mode. If the alarms are left in service they will only sound for a few seconds .
Its time to make a counter attack !

Offline Allen Higginson

  • Hero Member
  • *****
  • Posts: 1131
Haes conventinal panel
« Reply #4 on: January 31, 2008, 04:43:36 PM »
Hmmm,is its one of the Surveyors the walk test is a black push button on the pcb that you scroll through each zone and can only put one on at a time.
Reset quits test.

Offline Galeon

  • Hero Member
  • *****
  • Posts: 556
  • Dont ask me on here for advice , come down the Pub
Haes conventinal panel
« Reply #5 on: February 03, 2008, 01:58:31 PM »
Older surveyor panels worked as I indicated however theymade changes later on with only 1 zone under test as described by Buzzard905 , so it will be one or the other you have.