Following a visit during the construction stage of a leisure centre it has come to my attention that the compartment walls above the false ceiling on the 1st floor only have been constructed using a single layer of stone wool fire barriers. On further questioning it transpires that due to it being single thickness (incorrectly fitted) it only gives 15 minutes insulation not the 60 minutes as required by B3 of ADB.
B3 requires:-
The building shall be designed and constructed so that in the event of a fire, its stability will be maintained for a reasonable period. To inhibit the spread of fire within the building, it shall be sub-divided with fire resisting construction to an extent appropriate to the size and intended use of the building.
The guidance recommends 1 hour FR in terms of insulation and integrity for any compartment separation irrespective of the use of the rooms or space each side of the wall.
Fire consultants have argued that it meets the functional requirements based on the level of risk associated with the materials which exist on the unexposed side of the compartment wall i.e. cabling.
The temperature on the non fire side is estimated to be 300 degrees centigrade at 60 minutes. 165 centigrade at 17 minutes
Now I understand the rationale behind the argument and in all probability the fire may be through the roof before it’s through the wall and, whilst the cabling may not burn, will it melt and fall, even if it is on trays? Potentially hampering firefighters.
We have also given the advice to contacting the insurance company – but all they ask is does it comply with the RRO?
My thoughts are that whilst carrying out an audit the omission may not have become apparent but, following a fire where the compartment wall may have failed and potentially injuring or worse. Therefore, the potential for prosecution may be there.
Does anybody have any views?