It is all down to risk assessment and what is required and reasonable in the circumstances ( the BS's are not law). If you are having problems with misuse of a system down to the occupancy or area it is in, then you have to adapt to suit.
A manual override button may be provided, adjacent to the doors secured by electronic locks. but if there is a problem with the occupants ( may be vandalism or mental health issues), provided it is documented in the fire risk assessment, strategy and included in any staff/occupant training and information, you do not require the ‘green’ override box, only the fire alarm call point. Where activation of call points by Occupant/ residents is a problem, consideration should be given to providing measures such as ( in order of increasing technical requirements);
a. Lift flaps that prevent call point activation unless the flap is lifted, which is the least expensive option.
b. Further measures may utilise devices that activate a localized audible warning when a flap is lifted prior to call point activation.
c. In severe cases where the above measures prove insufficient ( usually mental health accomodation), a risk assessment should be undertaken to determine the impact of changing vulnerable break-glass call points to key-operated units that can be activated only by staff with ‘alarm keys’. Where ‘key operated alarm’ systems are provided as item c, included with the normal electronic locking conditions, there must also be the appropropriate procedures and safeguards etc.