Author Topic: Ems Panels  (Read 7098 times)

Offline jon b

  • Newbie
  • *
  • Posts: 20
Ems Panels
« on: February 29, 2008, 11:48:45 AM »
we have just had a radio system commissioned and the eng was saying that they do not allow anybody else to programme any cause and effects onto the system and if we did have to require any programming for the cause and effects that they would have to visit site and we would be charged for this . does this mean that ems is a closed protocol and has anybody else had this problem and what do other people think about ems systems

Offline Paul Field

  • Newbie
  • *
  • Posts: 3
    • http://www.w-fp.co.uk
Ems Panels
« Reply #1 on: February 29, 2008, 12:55:36 PM »
Hi jon,
The system is not closed protocol, what the EMS engineer may have meant is that the standard 5000 Firepoint panel cause and effects have their limits and if you need anything which is not standard then EMS have to build it in to the software before it leaves the factory. They can sometimes come to site with an upgrade if required. The standard panel can have delays and other cause and effects done on site.
In our experience 99% of the applications don't need any additional software upgrades if you want to make changes, although this may be down to the planning that goes in to the system prior to going to site, i.e. asking for co-incidence software etc
If you need help with the system please contact me on http://www.w-fp.co.uk/contact-us.html or via my email paulfield@w-fp.co.uk
Regards Paul

Graeme

  • Guest
Ems Panels
« Reply #2 on: February 29, 2008, 04:50:38 PM »
you could argue it was closed protocol as their devices will only work with their panel and vise versa

Offline Paul Field

  • Newbie
  • *
  • Posts: 3
    • http://www.w-fp.co.uk
Ems Panels
« Reply #3 on: February 29, 2008, 04:57:55 PM »
You have a point, but I think that Jon meant that it was not open to be worked on such as ADT/Siemens etc as far as the software is concerned.

Offline David Rooney

  • Hero Member
  • *****
  • Posts: 891
    • http://ctafire.co.uk
Ems Panels
« Reply #4 on: March 01, 2008, 03:15:04 PM »
If you are using mk 3 panels then there is some complicated c&e software called SGC.

EMS do not generally release this software as its bloody complicated and easy to cock up.

Having said that, we have the SGC due to the number of systems we look after.

You can do a reasonable amount with the panel, what are you trying to achieve ??

And talking of EMS, has anyone had problems with alkaline cells leaking (specially in detectors) that causes damage.??
CTA Fire - BAFE SP203 - F Gas Accredited - Wireless Fire Alarm System Specialists - Established 1985 - www.ctafire.co.uk
Natural Born Cynic

Graeme

  • Guest
Ems Panels
« Reply #5 on: March 02, 2008, 05:33:19 PM »
Did a 4.5 year battery replacement before Xmas as  detector had reported int sig fault. Found leaking batteries that damaged the detector.Several other of the detectors also had leaking batteries.

Offline FireStopper

  • Newbie
  • *
  • Posts: 6
Ems Panels
« Reply #6 on: March 02, 2008, 09:36:13 PM »
Quote from: Graeme
Did a 4.5 year battery replacement before Xmas as  detector had reported int sig fault. Found leaking batteries that damaged the detector.Several other of the detectors also had leaking batteries.
Do you want to name and shame the batteries?... I am interested as an engineer working in the fire systems industry.

Offline Paul Field

  • Newbie
  • *
  • Posts: 3
    • http://www.w-fp.co.uk
Ems Panels
« Reply #7 on: March 03, 2008, 09:36:06 AM »
Hi David, About the battery leaking, they do crop up occassionally although we have not had many over the years. I have not noticed any increase with that particular issue recently.

Offline David Rooney

  • Hero Member
  • *****
  • Posts: 891
    • http://ctafire.co.uk
Ems Panels
« Reply #8 on: March 03, 2008, 12:18:42 PM »
Well all the batteries we have had leaking are the Duracell Pro Cell supplied by EMS.

We've probably had 20 odd devices in the last six months and ofcourse EMS won't accept it as a warranty issue unless we now provide the complete system log from the day the device was installed to prove it hasn't been tampered with.
CTA Fire - BAFE SP203 - F Gas Accredited - Wireless Fire Alarm System Specialists - Established 1985 - www.ctafire.co.uk
Natural Born Cynic