Author Topic: Wall Cladding- Class O??  (Read 7594 times)

jakespop

  • Guest
Wall Cladding- Class O??
« on: July 12, 2010, 10:44:57 AM »
Has anyone any information on whether "Altro Whiterock" satisfies Class O surface spread of flame rating? The information I have is that it satisfies Clsss 1 of BS 476 and Class O of BS 476 Part 6. What is difference?

Offline Tom Sutton

  • Hero Member
  • *****
  • Posts: 2287
Re: Wall Cladding- Class O??
« Reply #1 on: July 12, 2010, 03:06:26 PM »
From what I understand jake Class "O" is a definition which only applies to Building Regulations (ADB)

Appendix A Para 13

The highest National product performance classification for lining materials is Class 0. This is achieved if a material or the surface of a composite product is either:

a. composed throughout of materials of limited combustibility; or

b. a Class 1 material which has a fire propagation index (I) of not more than 12 and sub-index (i1) of not more than 6.

Note: Class 0 is not a classification identified in any British Standard test.


To check if its class O then you will require the test results.

All my responses only apply to England and Wales and they are an overview of the subject, hopefully it will point you in the right direction and always treat with caution.