Two storey nursing home - lifts
« on: August 14, 2008, 12:58:03 PM »
Is it acceptable for lift shafts to open into the loft space with no capping/closing.
I can stand in the loft and see the lift going up and down.

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Two storey nursing home - lifts
« Reply #1 on: August 14, 2008, 01:47:12 PM »
If the loft space extends over the accommodation no it should be enclosed - walls should be 1 hour fire resistance with a half hour access door. If it is in its own little roofspace over the lift shaft and staircase only its not likely to be a problem.

Is the building less than a year old - if so refer to Buildng control.

PS same applies to staricase walls and compartment walls - these should extend to roof and any roof space bigger than 20 m should be subdicided with cavity barriers.

Offline John Dragon

  • Full Member
  • ***
  • Posts: 189
Two storey nursing home - lifts
« Reply #2 on: August 14, 2008, 08:29:06 PM »
Thanks for that, building is brand new, I have found quite a lot of other probs too. (not my job, I am only a fire alarm engineer, but something seems to be a bit rotten here!

Offline Izan FSO

  • Jr. Member
  • **
  • Posts: 60
Two storey nursing home - lifts
« Reply #3 on: August 14, 2008, 08:45:42 PM »
Quote from: John Dragon
Thanks for that, building is brand new, I have found quite a lot of other probs too. (not my job, I am only a fire alarm engineer, but something seems to be a bit rotten here!
Building Control it is then!!!