Author Topic: Domestic Sprinkler Testing  (Read 3698 times)

jakespop

  • Guest
Domestic Sprinkler Testing
« on: October 14, 2008, 09:57:30 PM »
I have a client who has a domestic sprinkler system and is asking if there are specific tests required for them. The installer told him to occasionally check the pressure gauge  but there was no mention of any periodic maintenance. Is there any British Standard guidance?

Graeme

  • Guest
Domestic Sprinkler Testing
« Reply #1 on: October 14, 2008, 10:01:58 PM »
Bs 9251

jakespop

  • Guest
Domestic Sprinkler Testing
« Reply #2 on: October 15, 2008, 01:07:47 PM »
I dont have a copy of BS yet. Can anyone give me a precis of any regular  test reqs please??

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Domestic Sprinkler Testing
« Reply #3 on: October 15, 2008, 03:20:18 PM »
Annual inspection and test by competent person-

1-heads ok and not impeded,
2-flow rate tested for 1 minute at drain and test valve,
3- audible alarm alarm remains effective and audible throughout
4- no unauthorised modifications to system.
5- Visual test for leaks.
6- Stop valve exercised.
7- If trace heating provided check operation.  
8- Alarm panel battery and power supply.
9- complete log book.