Simple answer, no its not acceptable to test the panel by taking off the pipe and testing it that way - you should be testing from the end point (if you can) / as many sample points as you can get to , and document the holes tested as best as you can.. Just in case of the holes is blocked - if there was a real fire and its found the holes have been blocked for some time, i imagine you could be in a bit of trouble.
Also, dont use the solo smoke.. you should be testing with something that you burn to get a accurate test - and you may find the unit may not even go off using solo aerosol smoke..
I'd recommend you get a smoke pole that holds the smoke sticks, I use a Hochiki one which you light the stick in the bottom, and extend the pole out to the sample point - in fact I think it goes higher than the solo poles.