Author Topic: Extinguishers. Are they a legal requirement?  (Read 15272 times)

Offline AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2479
    • http://www.firewizard.co.uk
Re: Extinguishers. Are they a legal requirement?
« Reply #15 on: November 24, 2008, 11:35:11 PM »
I know of three cases in the last 10 years due to poor maintenance - one serious injury & two fatal.

- Cartridge ANSUL powder Extinguisher with rusty base, but in date exploded & shot up with fatal head injuries
- CO2 being serviced with no horn or pin, fell off, landed on the valve, turned into a rocket went through a roof and caused fatal head injuries
- Cartridge water 'serviced' and not long after used on a hot works fire, bottom blew out, resulting in fractured wrist and dislocated shoulder. The engineer has serviced a couple of hundred of extinguishers at 4 different customer sites in one day

Classics illustrated on the cover of the old 90's BAFE brochure;
- Nu-swift BC powder model 1604 (the old inverse hourglass shaped strike knob one), serviced by poorly equipped engineer - he had the sealing plugs, but not the equipment to go with it so he drilled and soldered a Schroeder valve in the side
- Three riveted total discharge 2 gallon waters 'serviced' by in house maintenance team, beautifully rusted through the prolin & zinc linings and then recharged with 150g CO2 cartridges from 20lb powder extinguishers (which have the same size body). When used on a fire, one split, the other two holed and all fired rivets all over the place like bullets
- The last photo doesn't count as it was condemned, but the customer insisted on keeping it & the bottom blew out when used





Plus several 'failure to operates' that fortunately didn't lead to injury.
Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36

Offline jokar

  • Hero Member
  • *****
  • Posts: 1472
Re: Extinguishers. Are they a legal requirement?
« Reply #16 on: November 25, 2008, 10:19:14 AM »
Thomas, Article 17 starts with those mercurial words, Where Necessary.  Therefore, if you purchase extinguishers elsewhere then they are to be maintained where necessary.

Offline Thomas Brookes

  • Sr. Member
  • ****
  • Posts: 290
Re: Extinguishers. Are they a legal requirement?
« Reply #17 on: November 25, 2008, 11:02:16 AM »
I disagree, once you have extinguishers in a commercial premise with staff they have to be maintained to the manufactures guidance aswell as RR(FS)O and the The Workplace (Health, Safety and Welfare) Regulations 1992 section 5 (maintenance of the workplace) and in this one it does not state where necessary it says "shall be maintained". It will also somewhere under pressurised vessels say something as well, but I carn't be that bothered to go that deeply.

Back to what I said earlier, "Its a brave person, who when doing a fire risk assessment says there is no need for any firefighting equipment at all".

Yes there possibly are times but I can not think of many where no fire equipment or detection would be needed at all, and to make a sweeping statement on a forum read by many hundreds of people without the knowledge of FRA system is dangerous to say the least.

So on record jokar are you saying " No one needs fire extinguishers and no one should have them maintained if they have some"
I refuse to have a battle of wittts with an unarmed person.

Offline jokar

  • Hero Member
  • *****
  • Posts: 1472
Re: Extinguishers. Are they a legal requirement?
« Reply #18 on: November 25, 2008, 01:14:39 PM »
The FRA will take into account the hazrads and risks in the premises and come up the the outcome based solutions in an appropriate action plan.  If one of the outcomes for a life safety FRA is no extinguishers then so be it.  There may well be FFE in place that is not and can not be used by staff or residents in which case do not have them.

As regards the maintenance issue, you have choices, do not have extinguishers, have them by purchasing them yourself and disposing of them within their specified time frame and buying more or have a maintenance contract with a provider.

My question will be what do you want the extinguishers for and who will use them.

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Re: Extinguishers. Are they a legal requirement?
« Reply #19 on: November 25, 2008, 01:44:55 PM »
Those who are  of the opinion that fire extinguishers absolutely must be provided in premises, regardless of the circumstances, must also be of the opinion that heat and smoke detection is also provided, regardless of the circumstances.
Art 13 - (1) (a) .... appropriate fire-fighting equipment and with fire detectors and alarms; .......
We're not Brazil we're Northern Ireland.

Offline Thomas Brookes

  • Sr. Member
  • ****
  • Posts: 290
Re: Extinguishers. Are they a legal requirement?
« Reply #20 on: November 25, 2008, 02:56:16 PM »
All im am not saying every place has to have loads of extinguishers or detectors, that is down to a FRA.

The point im trying to get over is that no one can make a statement of extinguishers are not a legal requirement & there is no Law to say they have to be maintained.

Because some places it would be law to have such equipment and some it wont, also if you have got them and employees it is LAW to have them maintained, and this is where a lot of the people trained only in Fire Risk Assessments fall down, It may say in the RR(FS)O maintenance where necessary but in the  Workplace (Health, Safety and Welfare) Regulations 1992 it states equipment must be maintained. So you may be advising people under The RRFSO you only need maintain where necessary how ever under other health and safety laws it states if youve got the equipment it must be maintained. So yes your client may not get prosicuted under the RRO but may be under the workplace regs or some other regs.

All im saying is every case is different and no one can say every case does or does not have to have extinguishers.

I refuse to have a battle of wittts with an unarmed person.

Offline JC100

  • Full Member
  • ***
  • Posts: 126
Re: Extinguishers. Are they a legal requirement?
« Reply #21 on: November 25, 2008, 03:33:11 PM »
All im am not saying every place has to have loads of extinguishers or detectors, that is down to a FRA.

The point im trying to get over is that no one can make a statement of extinguishers are not a legal requirement & there is no Law to say they have to be maintained.

For residential buildings, BS 5588-1 says that extinguishers are not a legal requirement but desirable.
It does state however that they should be installed and maintained to BS 5306-3.

So yes, someone can state that they are not legally required if talking about residential buildings. As for saying don't maintain them...i haven't seen any documentation saying dont so i'd agree with what you are saying.

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Re: Extinguishers. Are they a legal requirement?
« Reply #22 on: November 25, 2008, 04:49:27 PM »
All im am not saying every place has to have loads of extinguishers or detectors, that is down to a FRA.

The point im trying to get over is that no one can make a statement of extinguishers are not a legal requirement & there is no Law to say they have to be maintained.

Because some places it would be law to have such equipment and some it wont, also if you have got them and employees it is LAW to have them maintained, and this is where a lot of the people trained only in Fire Risk Assessments fall down, It may say in the RR(FS)O maintenance where necessary but in the  Workplace (Health, Safety and Welfare) Regulations 1992 it states equipment must be maintained. So you may be advising people under The RRFSO you only need maintain where necessary how ever under other health and safety laws it states if youve got the equipment it must be maintained. So yes your client may not get prosicuted under the RRO but may be under the workplace regs or some other regs.

All im saying is every case is different and no one can say every case does or does not have to have extinguishers.


What about Article 17 - Maintenance. Where equipment, facilities and devices are provided they must be suitably maintained. Does that not cover it?
We're not Brazil we're Northern Ireland.

Offline nim

  • Jr. Member
  • **
  • Posts: 79
Re: Extinguishers. Are they a legal requirement?
« Reply #23 on: November 25, 2008, 07:29:06 PM »
There is also no need to buy from a Company and have a maintenance contract.  You can buy from a shop or over the internet.

You either have had a really bad experience with an extinguisher maintenance/supply company or you genuinely think that nothing can go wrong with a fire extinguisher.

 
have them by purchasing them yourself and disposing of them within their specified time frame and buying more
What is the specified time frame for a fire extinguisher? Assuming that the majority/all users of fire extinguishers are not competent when will they know when the extinguisher has reached the end of it’s “specified timeframe”.

Is it when it fails to work? Too late if they have a fire and then cheap fire extinguisher they bought from the internet or decided not to maintain because they were told they didn’t need to have it maintained then becomes an expensive doorstop.

My question will be what do you want the extinguishers for and who will use them.
Agreed everyone on discovering a fire should raise the alarm, evacuate the building and call the fire brigade. That shouldn’t stop anyone having fire extinguishers and having them maintained.

But if a FRA says extinguishers are required why would you want to advise anyone to not use a company who will commission, install and maintain extinguishers to BS5306 Part 3?  Are you just trying to gain brownie points by giving them what you consider is inside information that they could save some money by using an internet supply company or not have them maintained?




Offline jokar

  • Hero Member
  • *****
  • Posts: 1472
Re: Extinguishers. Are they a legal requirement?
« Reply #24 on: November 25, 2008, 08:15:27 PM »
Nim, neither, the discussion is about the legal requirement for extinguishers.  I do not believe such a requirement exists.  The outcomes of an FRA will decide on the control measures that are a solution to the hazards and risks in any premises.  The RP has the choice to either buy and maintain, to buy and not maintain or to lease from a compnay on a maintenance contract.  The RP choice and not mine and their choice is in part down to costs.

Offline Thomas Brookes

  • Sr. Member
  • ****
  • Posts: 290
Re: Extinguishers. Are they a legal requirement?
« Reply #25 on: November 25, 2008, 09:01:36 PM »
The Government guide books state you should install fire extinguishers where required in accordance of BS5306.

The whole point of FRA is to get away from prescription.

I have pasted a report below Case 1 from a company fined £35k for not maintaining their fire equipment properly, part of it was for lack of maintennace of fire extinguishers, may be you can get them a refund as extinguishers arnt needed.
And Case 2 at the bottom he would love to here from you because he was fined over £10k including for not providing fire fighting equipment and seeing you say he does not need any may be you can get him a refund as well.

CASE 1
total of more than £35,000 after serious breaches of security were discovered following a fire.

Mill House Inns Trading admitted breaking fire safety regulations at the White Swan Hotel in Arundel in Sussex, during a hearing before Worthing Magistrates.

The court heard that fire broke out at the hotel in March 2007 and 10 guests trapped in their bedrooms had to be rescued by fire fighters. No serious injuries were reported.

A subsequent investigation by fire officers revealed a series of lapses of fire safety security.

According to evidence given before the court the fire alarm panel had been switched to silent, fire doors had been wedged open, staff had not received adequate fire safety training, fire alarms had not been tested correctly, and there was no overall emergency plan.

The company was fined £25,000 with £11,000 costs.

After the case director of community protection Trevor Pilcher said: "This hotel had the right physical precautions in place like smoke detectors, self-closing fire doors, emergency lighting and fire extinguishers but all that becomes ineffective if the management of the fire precautions isn't good enough.”



CASE 2
10 January 2008

The owner and landlord of a HIMO (house in multiple occupation) was fined more than £10,000, including costs of over £1,900, after pleading guilty yesterday to six charges relating to inadequate fire safety standards.

Proceedings were brought against Aftab Hussain after he failed to comply with an enforcement notice issued by Buckinghamshire Fire & Rescue Service in December 2006 under the Regulatory Reform (Fire Safety) Order.

The notice was issued because fire safety inspectors identified a number of fire safety shortfalls at the property in Conegra Road, High Wycombe, including:

Failure to provide adequate fire detection and emergency lighting


Failure to adequately protect the means of escape


Failure to provide adequate fire fighting equipment
He was prosecuted because he failed to put them right within the timescales set.

Mr Hussain pleaded guilty to all counts at High Wycombe Magistrates Court and was fined a total of £10,377.68, including more than £1,900 costs.

The Magistrate commented on the serious nature of the offences and praised the quality of the evidence presented by Buckinghamshire & Milton Keynes Fire Authority.

Station Manager Graham Field, Fire Safety Team Leader for Wycombe and South Bucks, said afterwards: “This case clearly demonstrates how our safety officers are inspecting relevant buildings and applying the law to help ensure the safety of our community. 

“Prosecution is only considered in the most serious cases or otherwise as a last resort, but will be persued with the utmost vigour when necessary”.

The law under which he was prosecuted applies to nearly all premises, with the exception of single private dwellings. In HIMOs, it applies to common areas of the building, where a “responsible person” must ensure adequate fire safety standards through a process of fire risk assessment.

Chris Bailey, Group Manager Prevention, said: “Although this happened in High Wycombe, we would like it to act as a timely reminder to people throughout Buckinghamshire and Milton Keynes that these regulations are there to make people safer.

“We will help people in any way we can to comply with them, but sometimes we need to take legal action.”

Chief Fire Officer Damian Smith said: “This case highlights the dedication and professionalism of our fire safety team, who are committed to making sure that buildings of this type are safe and fit for purpose.

“I would like to congratulate the team for the tremendous work it has done to bring about this prosecution.”

Since the Regulatory Reform (Fire Safety) Order (RRO) came into force in 2006, Buckinghamshire Fire & Rescue Service has issued around 100 notices restricting the use of part or all of a building or requiring fire safety improvements.


I refuse to have a battle of wittts with an unarmed person.

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Extinguishers. Are they a legal requirement?
« Reply #26 on: November 25, 2008, 09:41:22 PM »
I guess Thomas we will always differ on our views on this and debate is a good thing.
The cases you have posted are clear enough. But looking at the spectrum of the offences- there is a significant range of issues. Would the case have been brought over the extinguishers in isolation? Almost certainly not. Would the case have been brought over the means of escape issues in isolation- Absolutely.
When the policeman pulls you over for drunk driving he will check your car and if you are also driving with bald tyres and your number plate lamp not working he will chuck the book at you. All offences will be brought to the attention of the court and fines will be issued for all if found guilty. But had your  tyres been good and had you been sober you may not even have been pulled up for the defective light. 

Offline nim

  • Jr. Member
  • **
  • Posts: 79
Re: Extinguishers. Are they a legal requirement?
« Reply #27 on: November 25, 2008, 09:48:16 PM »
If someone asks whether they need fire extinguishers I will always tell them to have a FRA carried out. If I were to see a FRA which specified that extinguishers were not required or that maintenance of extinguishers were not required on premises which I thought required extinguishers or maintenance then I would always raise my concerns.

Nim, neither, the discussion is about the legal requirement for extinguishers. 
It was you who mentioned that "There is also no need to ................have a maintenance contract." and also  "disposing of them within their specified time frame and buying more".

I understand your reference to "Where neccessary". It just seems as though your advice seems to be that if a FRA recommends fire extinguishers then to employ someone competent to commission, install and maintain extinguishers is either a waste of time  or money or something else. You are obviously not prepared to divulge

With regard to  prosecutions. The first imprisonment.
http://forum.fire.org.uk/index.php?topic=3251.msg37583#msg37583

Chris Houston

  • Guest
Re: Extinguishers. Are they a legal requirement?
« Reply #28 on: November 25, 2008, 10:15:58 PM »
I work for an insurance broker / risk management consultancy.

When I used to work for an insurer and clients asked me if they needed extingiushers I told them yes and it was a requirement of insurance.

Now when clients ask me, I tell them it will be a requirement of thier insurer and they should do it for property protection, health and safety and to avoid litigation.

In my several years in the insurance industry, I have yet to hear of an injury claim associated with a fire extinguisher. 

I have also been to numerous sites where fires have been put out safely in their early stages by extingiushers.

I also volunteer for the British Red Cross and every few months end up at a domestic fire where people tend to be found standing outside a burnt out house.  I'd say about 90% of the time they have tried and failed to put out fires with pots of water and garden hoses.  People will try.  I'd suggest giving them the tools and training to know how to do it properly and when not to even try.

Offline AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2479
    • http://www.firewizard.co.uk
Re: Extinguishers. Are they a legal requirement?
« Reply #29 on: November 25, 2008, 11:18:59 PM »
All the extinguisher fatals and serious injuries I referred to have lead to legal cases & the injury one cost FPS a lot of money in compensation on top of their penalties.

There are 'maintenance free' extinguishers around with a shelf life, traditionally these have been aerosol BCF & Powder extinguishers with no gauge (e..g Firemaster & Fireblitz) that a service engineer can only do the visual user check and thus nothing worthy of a service fee or label. If risk appropriate and within expiry dates I will accept these without a service label.

However, the disposable industry is getting to advanced for it's own good. The addition of gauges (that need verification) such as in most current Firemaster, Vanguard/guardian & 'pound shop' type equipment and the ability to refill means that essential components that are beyond user checks exist (gauge verification) and some apparently service free extinguishers could be argued to require maintenance.

Where risk appropriate & when cost is a realistic factor in compliance I have no problem in suggesting 5 year life disposable powders and make the user fully aware of the pro's & con's (price often wins over the minimal likelihood of ever being used and causing secondary damage though)
Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36