Good luck with that
Sorry to be sceptical but ive heard many a fire officer and supposed risk assessor suggest that a resident check the system daily and do fire alar tests weekly
Let me introduce you to the real world PS.
Yeah you might convince a resident to check your fire alarm system daily and test it weekly - and bully for you if they do that.
Most residents however will say they want a fee for doing it. And what if that resident goes on holiday ? Who tests it then?
Look at the British standard . As per usual it is written by people who have no idea of what goes on on planet earth. But hey they get paid well so whats the problem?
Read the BS. It does not state a call point should be tested weekly and anyone who suggests it does had best question their competency. And actually had better find another job because they obviously haven't the first clue what they are doing.
Better still ask a Magistrate or a Judge what they think.
Don't think anyone has said that call point should be tested weekly CF3.
44.2
Recommendations for weekly testing by the user
When testing the fire detection system, there may be a need to isolate ancillary outputs.
The following recommendations apply:
a) Every week, a manual call point should be operated during normal working hours. It should be
confirmed that the control equipment is capable of processing a fire alarm signal and providing an output
to fire alarm sounders, and to ensure that the fire alarm signal is correctly received at any alarm
receiving centre to which fire alarm signals are transmitted. It is not necessary to confirm that all fire
alarm sounder circuits operate correctly at the time of this test.
NOTE 1 It is essential that any alarm receiving centre is contacted immediately before, and immediately after, the weekly test
Agree though that daily and weekly user checks are very much OTT.