Was the building convertion passed by Building Control especially with regards to the bedroom being an inner room condition?
The building conversion took place in 1977, well before I bought the flat and, although I know there was planning permission , I do know if there was any stipulations with regard to fire safety
Not sure what the Building Control standards were then but maybe someone older than me might be able to comment. Sleeping inner room probably acceptable then with a window of unobstructed opening not less than 850 mm by 500 mm with the bottom of any window opening not more than 1 100 mm above the floor of the room in which it is situated.
Current guidance says:-
Where the inner room is any other type of habitable room (for example a living room, sleeping room, workroom or study) it should only be accepted if:
• the inner room has access to a suitable door opening onto an alternative safe route of escape, or it is situated on a floor which is not more than 4.5m above ground level and has an escape window leading directly to a place of ultimate safety;
• an adequate automatic fire detection and warning system is in place (see paragraphs 22-25); and
• a fire-resisting door of an appropriate standard is fitted between the inner and outer rooms (typically FD30S standard for non-high-risk outer rooms).