Author Topic: 7273 and location of detectors  (Read 72460 times)

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Re: 7273 and location of detectors
« Reply #105 on: July 27, 2009, 11:06:11 PM »

Addressable systems

If the interfacing is to be carried out at the panel then the requirements are as the non-addressable system above.

If the interfacing is on the addressable loop then an interface that is loop powered energised in it's normal condition is required (Hochiki manufacture such a device). With other interfaces it will be necessary to also wire a simple relay powered from the loop and wire the contacts of both relays in series to the fail-safe BS7273-4 signalling relay.


I would welcome comments from those that are interested in the above summary so that we can 'tweak' it until it is correct and understandable to everyone.

Hello Wiz...

Seems about right to me.... my only question is still regarding the action of the Hochiki I/O - do you know if it changes state on "software failure" and what that means?

Re the "other interfaces" I've also been advised by Apollo in the past not to power relays directly from a loop... but just to be clear, are you suggesting a relay connected to the loop (permanently energised) in turn connected to its own closed contacts (open on power fail) in series with the normally closed on the I/O (the "part 4 relay") so if either one opens the magnet releases?


Dave, my understanding is the 'software fault' monitoring is a standard requirement of the current EN/BS for control panels. What this actually covers, I don't know because I don't design control panels. Obviously, there is some sort software fault monitoring on control panels and this will give a panel 'fault' condition.

So the C&E would be that any fire or fault condition monitored by the the cie would operate the addressable loop output interface. If the panel fault condition also operated on disablements then no further action is required. (although it seems the disablement function giving a fault condition isn't a standard requiremnt of the EN/BS for panels)

However, most addressable panels have a seperate disablement warning (i.e doesn't necessarily create the fault condition) so in this case the C&E would be either a fire/fault/disablement condition on the cie would operate the addressable loop output interface.

To cover the requirement whereby the interface fail-safes on loop power failure we would need an interface that was energised on in the normal condition and fail-safe de-energised on loop power failure. Evidently one of the Hochiki models does this.

Evidently, the Apollo output units don't do this because they have more of a 'flip-flop' style relay which might stay in it's last state even after power disconnection. In this case if we use a simple standard relay kept energised from the loop and wired it's contacts in series with the addressable output unit, either relay changing state (the addressable on fire/fault/disablement data received , and the standard on power failure) will provide the signalling circuit to our 'part 4' system. I note your comments about not powering a standard relay coil from the loop. I could see that back emf etc. might cause problems. I've powered other stuff from the loop with no problems but never relays. I'm going to talk to Apollo about this. It might mean a 'special' relay or relay circuit is going to be required.

Going back to the software fault, it would seem that this doesn't have to include loss of data on the loop. I thought that it might. Buzz previously highlighted that the BS doesn't specifically mention it. So I think he is right. We just need to know when the panel detects a 'software' fault as determined in the panel standards.

This BS recommendations don't seem to provide a perfect fail-safe situation. But does this matter to us? At this time we're more interested in finding out how to make the BS work rather than any potential failings with it.

Graeme

  • Guest
Re: 7273 and location of detectors
« Reply #106 on: July 28, 2009, 02:05:20 PM »

I have the solutuion to disablements ;D

set up all panels in future with restricted access so the end user cannot disable anything only an Engineer.

So if a customer gets a fault,the fault relay will shut the doors and he will have to call out an engineer of he wants them to stay open again.

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Re: 7273 and location of detectors
« Reply #107 on: July 28, 2009, 02:41:41 PM »

I have the solutuion to disablements ;D

set up all panels in future with restricted access so the end user cannot disable anything only an Engineer.

So if a customer gets a fault,the fault relay will shut the doors and he will have to call out an engineer of he wants them to stay open again.

Your'e getting desperate, Graeme! Next you'll be suggesting that we disable the end-users so they can't touch the fire panel!

I know your post was in jest, but disablements, even by an engineer, have to operate the release mechanism interface. Also I have found that there are a reasonable number of panels out there with disablement relays, but nowhere near all of them because it is evidently not a requirement of the cie design EN/BS.

By the way, the BS is only looking for disablements that are capable of affecting the correct operation of the release mechanisms, but I can't see anyone taking the time to wire/configure so that only if detectors a or b are disabled will door x release automatically, and only if detectors c, d or e are disabled will door y release automatically. I suspect that it in practice designers will just want any disablement to operate all release mechanisms.

Also we have found that there are a reasonable number of panels out there with disablement relays

I can't wait until the scaremongering about having to comply with this BS begins - I will enjoy watching the ensuing panic. I might even start the scaremongering myself, if I ever work out how to comply with all parts of the BS!

Offline David Rooney

  • Hero Member
  • *****
  • Posts: 891
    • http://ctafire.co.uk
Re: 7273 and location of detectors
« Reply #108 on: July 28, 2009, 03:55:36 PM »
So.... if you can set up a system eg 10 storey office block and in a quite simplistic scenario program detectors/callpoints to release doors on the floor of origin only - the detectors that are "capable of affecting the correct operation of the release mechanisms"....

does that mean that when testing as required in 7273-4...

22.1.1 Every week, a fire alarm signal(s) should be used to cause actuation of all release mechanisms. It should be confirmed that each
release mechanism operates correctly and that the doors close properly, unlock or revert to the fully open position, as appropriate.
This test should normally be carried out at approximately the same time each week.


...... you should then test a call point on every floor level once a week to prove the release "path" is fully working?
« Last Edit: July 28, 2009, 04:05:59 PM by David Rooney »
CTA Fire - BAFE SP203 - F Gas Accredited - Wireless Fire Alarm System Specialists - Established 1985 - www.ctafire.co.uk
Natural Born Cynic

Offline Allen Higginson

  • Hero Member
  • *****
  • Posts: 1131
Re: 7273 and location of detectors
« Reply #109 on: July 28, 2009, 04:16:59 PM »
So.... if you can set up a system eg 10 storey office block and in a quite simplistic scenario program detectors/callpoints to release doors on the floor of origin only - the detectors that are "capable of affecting the correct operation of the release mechanisms"....

does that mean that when testing as required in 7273-4...

22.1.1 Every week, a fire alarm signal(s) should be used to cause actuation of all release mechanisms. It should be confirmed that each
release mechanism operates correctly and that the doors close properly, unlock or revert to the fully open position, as appropriate.
This test should normally be carried out at approximately the same time each week.


...... you should then test a call point on every floor level once a week to prove the release "path" is fully working?

Two tests - one as per normal requirements on a different MCP and the other on a general alarm input (evac button??) that drops everything??

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Re: 7273 and location of detectors
« Reply #110 on: July 28, 2009, 04:23:54 PM »
So.... if you can set up a system eg 10 storey office block and in a quite simplistic scenario program detectors/callpoints to release doors on the floor of origin only - the detectors that are "capable of affecting the correct operation of the release mechanisms"....

does that mean that when testing as required in 7273-4...

22.1.1 Every week, a fire alarm signal(s) should be used to cause actuation of all release mechanisms. It should be confirmed that each
release mechanism operates correctly and that the doors close properly, unlock or revert to the fully open position, as appropriate.
This test should normally be carried out at approximately the same time each week.


...... you should then test a call point on every floor level once a week to prove the release "path" is fully working?


david, I think your question is answered in 22.1.2

Offline David Rooney

  • Hero Member
  • *****
  • Posts: 891
    • http://ctafire.co.uk
Re: 7273 and location of detectors
« Reply #111 on: July 28, 2009, 04:46:31 PM »
ooops.... sorry didn't get that far.....!
CTA Fire - BAFE SP203 - F Gas Accredited - Wireless Fire Alarm System Specialists - Established 1985 - www.ctafire.co.uk
Natural Born Cynic

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Re: 7273 and location of detectors
« Reply #112 on: July 28, 2009, 04:51:39 PM »
I have now identified a cie that runs XP95 that has the fire/fault/disable relays that would allow connection from the cie to the BS7273-4 system. I am told by the manufacturers that this cie complies with EN54 and so, according to what we have been told on this forum, will therefore monitor all the faults conditions required of the fire alarm system for this sort of system.

Furthermore I have identified a loop powered addressable output relay that runs on XP95 protocol that when used in conjunction with the cie mentioned above, will allow a special loop-powered interface to be used. The panel C&E programming software can be used to write a programme that will keep the interface enrgised in the normal condition and release it on either a fire, fault or device disabled condition. If the interface loses loop power it will fail-safe denergised.

I believe that the above is everything required to control Category A systems of BS7273-4

The C&E programming software also provides the ability to make the loop-powered output de-energise on single or groups of detection devices and for zones of detection devices etc.

I am willing to provide details of the cie, the 'special' addressable output relay and the required C&E programming to those who are interested.

However, I've learnt from some people on this forum that you shouldn't do anything for nothing and I'm therefore going to make a charge of £10 to each person who wants the info. All proceeds from this will be given to a charity of my choice.

If you are interested please PM me and I'll provide details of how you can pay to obtain this information.

David R, Buzz and Graeme - I have PM'd you a message

« Last Edit: July 28, 2009, 05:24:17 PM by Wiz »

Offline Buggy

  • Newbie
  • *
  • Posts: 18
Re: 7273 and location of detectors
« Reply #113 on: July 28, 2009, 05:06:40 PM »
...will you be sharing this information via a 'half day course'  ;D

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Re: 7273 and location of detectors
« Reply #114 on: July 28, 2009, 05:27:23 PM »
...will you be sharing this information via a 'half day course'  ;D

Very good! It could happen, you never know  ;)
« Last Edit: July 28, 2009, 05:33:35 PM by Wiz »

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: 7273 and location of detectors
« Reply #115 on: July 29, 2009, 10:09:55 PM »
Thanks Dr Wiz for your work on this. Whilst your technical analysis and proposed solution is above my head (and I guess the majority of my peers) it is very useful and enlightening. I have been ploughing through the document itself prompted by the issues you raise. It strikes me as an esoteric mix of information, partly founded on performance based standards which will not relate to anyone other than the designers of CIE or software protocols, with a broad base of  functional requirements founded on common sense to which I and my peers in fire risk assessment can relate but perhaps beyond the normal considerations of the equipment designer. It is of course most relevant to the M&E  design team for new buildings. Because the standard  is so dependent on the CIE and software protocols perhaps it would have been more widely understood if it had been part of the BS5839 or EN 54 series? 

To me it would be a  bit like a  highway code that instead of simply setting out  overall braking distances for the education of drivers also set out the technical performance for the cadence braking applied by the ABS system. 

Certainly whilst it raises essential considerations for the fire risk assessor, for use in assessing  everyday fire safety issues and problems  in existing premises with existing alarm systems (eg wedges in persistent use or old ladies being knocked over by fire doors) it would appear very difficult or expensive to achieve  BS7273 part 4 compliant solution.

Offline David Rooney

  • Hero Member
  • *****
  • Posts: 891
    • http://ctafire.co.uk
Re: 7273 and location of detectors
« Reply #116 on: July 30, 2009, 02:28:59 PM »
... Spot on K.... and from a contractors point of view, do we

a.  try and comply but lose the job as our costs are considered excessive, eventually declare ourselves bankrupt, hand back the sky dishes and put a dozen people on the dole

b.  not comply but sign a 5839 compliance certificate (may be slipping in a variation) like most other installers who most likely are ignorant of 7273 or don't care, rake in the profits and go and live in essex, apparently one of the safest area in the country?

« Last Edit: July 30, 2009, 02:43:51 PM by David Rooney »
CTA Fire - BAFE SP203 - F Gas Accredited - Wireless Fire Alarm System Specialists - Established 1985 - www.ctafire.co.uk
Natural Born Cynic

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Re: 7273 and location of detectors
« Reply #117 on: July 30, 2009, 03:28:50 PM »
Prof. K, I trust you had a nice holiday but I hope your post is not a criticism of BS7273-4! You might regret it if it is! (I can't tell if it was a criticism - using words such as esoteric is above my head - for an explantion of my poor educational standards please see below)

David, your fears are understandable, but you should look at the BS as an opportunity rather than a hinderance. If we ever get to understand it fully and know how to comply with it (and you know how hard we are struggling to do that!) then you will be one of the few that can install to that standard. In fact, you'll be able to start prompting the designers to include reference to BS7273-4 in their specifications, and really give the other installers something to think about!

I also thank you for your comments regarding the safety of Essex. I have lived in Essex for most of my life and my business has been based in that beautiful  ;) County for 28 years, partly servicing/installing but mainly now just supplying equipment, design & commissioning services and technical back-up to installers and I have undoubtedly 'raked in the profits'. Small as they are - I still rake madly and continuously!

I am therefore obviously entirely responsible for making Essex one of the safest areas in the Country!  :)
« Last Edit: July 30, 2009, 03:41:24 PM by Wiz »

Offline David Rooney

  • Hero Member
  • *****
  • Posts: 891
    • http://ctafire.co.uk
Re: 7273 and location of detectors
« Reply #118 on: July 30, 2009, 04:18:28 PM »

I am therefore obviously entirely responsible for making Essex one of the safest areas in the Country!  :)


God bless the humble modest engineers for they shall (or is it should) receive their badge of competency (following a risk assessment on working at heights) in heaven........!!