I am recommending an Aspirating Smoke Detectors on a listed building project where it serves both life safety and property protection (yes, insurers choose it over sprinklers) in addition to the aesthetic appeal. The building will have a very good management system.
However the potential users of the building will be smoking within the aspiration-protected areas (a fait accompli): obviously this will conflict with the early detection the system will afford.
We looked at different options of accommodating these things and arrived at incorporating a timer and relay logic where the system will have two sensitivity modes normal and smoking mode with push button in those areas where smoking will be taking place. Before smoking is started, the smoking mode (low sensitivity) will be activated by the push button and that will give the smokers certain time to smoke and will automatically return to normal mode upon elapsing of the set time.
all this sounds good, except it may take longer for the smoke particles to clear from the affected room (we'll be unable to use mechanical system to evacuate the particles) and therefore the system might be susceptible to false alarm upon returning to normal mode. This is the client's concern, as similar problem was encountered in one of their buildings. – We don’t want to set longer time for the smoking mode
I am wondering whether somebody in this forum has encounter similar problem and how s/he went about resolving it. And also if other members can help with idea on how to resolve or improve the above option or if there is a better solution out there. Any idea is welcome.