Am I correct in asking for dry risers to be pressure tested every year and visually inspected 6 monthly? Any views or opinions welcome.

Offline AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2492
    • http://www.firewizard.co.uk
Re: Dry Riser Testing
« Reply #1 on: November 06, 2009, 02:29:05 PM »
If being maintained as per the current BS, yes.

If you don't follow the BS you need to demonstrate that your alternative regime is suitable & sufficient.

Most office blocks where there is little risk of damage to outlets only bother with the annual test for example.