Author Topic: Are break glass call points normally intrinsically safe?  (Read 6182 times)

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Are break glass call points normally intrinsically safe?
« on: November 13, 2009, 01:31:25 PM »
Are break glass call points and sounders, normally intrinsically safe and if so how can one tell from the unit?
We're not Brazil we're Northern Ireland.

Offline Mike Buckley

  • Hero Member
  • *****
  • Posts: 1045
Re: Are break glass call points normally intrinsically safe?
« Reply #1 on: November 13, 2009, 04:14:10 PM »
The short answer is no. All electrical equipment for use in hazardous atmospheres should be marked with the group number for the range of gases it is dsigned for. There is a standard mark but I can't find it at the moment. If you have a look at the Dangerous Substances and Exposive Atmospheres regulations it should all be explained in there.
The presence of those seeking the truth is infinitely to be preferred to those who think they've found it.

Offline Allen Higginson

  • Hero Member
  • *****
  • Posts: 1131
Re: Are break glass call points normally intrinsically safe?
« Reply #2 on: November 13, 2009, 05:41:21 PM »
Nope - they will have an identification on them (Ex) and in the case of sounders operate at lower current than standard ones (this does limit the amount you can put on the circuit after the barrier and affects your dB output).
They are also more expensive!

Offline ps

  • Jr. Member
  • **
  • Posts: 88
Re: Are break glass call points normally intrinsically safe?
« Reply #3 on: November 13, 2009, 05:46:44 PM »
I've got a good guide to the regs I can send you if that's any help?

Offline ps

  • Jr. Member
  • **
  • Posts: 88
Re: Are break glass call points normally intrinsically safe?
« Reply #4 on: November 13, 2009, 05:51:15 PM »
Thinking about it you probably don't want all the gumph, just the following would be helpful

All equipment used in hazardous areas and which meet the requirements of the Equipment and Protective Systems Intended for Use in Potentially Explosive Atmospheres Regulations 1996 should be marked with:
•   a CE mark
•   the explosion protection symbol (as shown)
•   the equipment group and category
•   a G for an explosive atmosphere caused by gases or vapours or a D for explosive atmospheres caused by dusts
•   the name and address of the manufacturer
•   the designation of series or type
•   the serial number, if any
•   the year of construction.

Equipment manufactured to the appropriate standard should still be tested following installation and should be inspected regularly and maintained by a competent person.

The symbol won't cut and paste for me, but its a hexagon with the letters E and X inside"

Offline AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2492
    • http://www.firewizard.co.uk
Re: Are break glass call points normally intrinsically safe?
« Reply #5 on: November 14, 2009, 03:23:35 PM »
Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36

Offline ps

  • Jr. Member
  • **
  • Posts: 88
Re: Are break glass call points normally intrinsically safe?
« Reply #6 on: November 16, 2009, 10:04:31 AM »
very pretty! ;D

Midland Retty

  • Guest
Re: Are break glass call points normally intrinsically safe?
« Reply #7 on: November 16, 2009, 02:50:02 PM »
Cheers Anthony - can you send a bigger one?

Offline David Rooney

  • Hero Member
  • *****
  • Posts: 891
    • http://ctafire.co.uk
Re: Are break glass call points normally intrinsically safe?
« Reply #8 on: November 16, 2009, 05:43:57 PM »
Cheers Anthony - can you send a bigger one?


Have you got one in Braille you could fax ??
CTA Fire - BAFE SP203 - F Gas Accredited - Wireless Fire Alarm System Specialists - Established 1985 - www.ctafire.co.uk
Natural Born Cynic

Offline AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2492
    • http://www.firewizard.co.uk
Re: Are break glass call points normally intrinsically safe?
« Reply #9 on: November 16, 2009, 11:59:54 PM »
LOL! I was in a rush & it was the first link I found!
Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36