Author Topic: BS5306, part 8 - table 2  (Read 5995 times)

Offline Hi Tower

  • Jr. Member
  • **
  • Posts: 50
    • Hitower
BS5306, part 8 - table 2
« on: September 03, 2010, 09:18:32 AM »
It is detailed in table 2 of the above standard that the amount of wet chemical required to extinguish a cooking oil fire increases accordingly with respect to the surface area of the cooking oil vat; e.g. 0.06 square metres = 5F extinguisher, 0.27 square metres = 75F + 25F.  This makes sense until you reach the last example which states  0.40 square metres = 75F.  Why in this case where the surface area increases does the amount of wet chemical media required decrease?  Is it as simple as a misprint or am I missing something?


Offline deaconj999

  • Jr. Member
  • **
  • Posts: 96
Re: BS5306, part 8 - table 2
« Reply #1 on: September 03, 2010, 09:42:04 AM »
Good Question,

The more I looked, the more confusing it got. It must be a typo and not just one, if I try to reason the calculation regardless of derating it got worse.

Where's my Rubiks Cube.......

Online AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2489
    • http://www.firewizard.co.uk
Re: BS5306, part 8 - table 2
« Reply #2 on: September 03, 2010, 11:45:08 AM »
no, it refers to 2 x 75F.

Column one is area where two extinguishers are used.

Row 1 is therefore 2 x 5F
Row 2 2 x 15F
Row 3 2 x 25F
Row 4 a 75F + a 15F
Row 5 a 75F + a 25F
Row 6 2 x 75F

Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36

Offline deaconj999

  • Jr. Member
  • **
  • Posts: 96
Re: BS5306, part 8 - table 2
« Reply #3 on: September 03, 2010, 12:41:08 PM »
I get it now, thanks, although it would have been better put in a table like this maybe

Maximum surface area to be extinguished (m2)   Minimum Extinguisher(s) required
0.015                                                                       1 x 5F
0.02                                                                       1 x 15F
0.04                                                                       1 x 25F
0.06                                                                       2 x 5F
0.08                                                                       2 x 15F
0.11                                                                       1 x 75F
0.13                                                                       2 x 25F
0.24                                                                       1 x 75F + 1 x 15F
0.27                                                                       1 x 75F + 1 x 25 F
0.40                                                                       2 x 75F

Offline Hi Tower

  • Jr. Member
  • **
  • Posts: 50
    • Hitower
Re: BS5306, part 8 - table 2
« Reply #4 on: September 03, 2010, 01:21:23 PM »
Thanks AB
Like D999 says the table could be presented better, like shown - but thank you for the explanation