Author Topic: British Standards in relation to Emergency Lighting.  (Read 5724 times)

Offline Tom Sutton

  • Hero Member
  • *****
  • Posts: 2287
British Standards in relation to Emergency Lighting.
« on: September 25, 2010, 10:37:22 PM »
I recently had an enquiry regarding an emergency lighting system using LED's fed by a CBU and mains supply. The next day I was in my local shopping centre and they had LED's attached to the stair guardrail similar to the enquirer and was wondering if they are becoming more popular for emergency lightning?

However my main problem was the relationship between BS 5266-1:1999, BS EN 1838:1999/BS 5266-7:1999 and BS EN 50172:2004/BS 5266-8:2004.

Part 1 has to be read in conjunction with part 7 and part 8 partially supersedes part 1, which has been revised to remove requirements conflicting with BS EN 50172:2004. Does this mean you ignore part 1 and read part 8 in conjunction with part 7 or do you have to study all three? Apart from the confusion this causes, you have pay for three documents instead of one.

My question does anybody know if the are any plans to rationalise this situation because apart from the cost understanding BS's is hard enough.
All my responses only apply to England and Wales and they are an overview of the subject, hopefully it will point you in the right direction and always treat with caution.

Offline deaconj999

  • Jr. Member
  • **
  • Posts: 96
Re: British Standards in relation to Emergency Lighting.
« Reply #1 on: September 26, 2010, 05:48:13 PM »
Tom,

Dead Right BSs are confusing but I noticed you mention 5266-1 1999, which was superseded by the 2005 edition.

Don't know if this helps but the scope of the 2005 says

The 1999 edition of this standard no longer covered the levels of illumination
required as these are dealt with in BS EN 1838:1999 (also numbered  
BS 5266-7:1999). References to BS EN 1838:1999/BS 5266-7:1999 are made at
the relevant points in the text.
The standard has now been revised again to remove recommendations and
guidance on the characteristics of emergency lighting systems that are now
specified in BS EN 50172:2004 (also numbered BS 5266-8:2004). References to
BS EN 50172:2004/BS 5266-8:2004 are made at the relevant points in the text.
This part of BS 5266 has thus become a base document, which, in addition to
giving basic guidance on emergency lighting, provides a guide to navigation of the
other parts of the BS 5266 series.
This revision of BS 5266-1 is applicable to cinemas, and also to other premises
used for entertainment, some of which were excluded from the 1999 edition.
BS EN 50172:2004, 4.1 specifies compliance with the wiring rules given in
HD 384/HD 60364. The UK applicable parts of HD 384/HD 60364 are
implemented in the IEE Wiring Regulations (BS 7671).
This revision of BS 5266-1 incorporates changes necessitated by the publication
of BS EN 50172. It does not represent a full review or revision of the standard,
which will be undertaken in due course.

Offline colin todd

  • Hero Member
  • *****
  • Posts: 3473
  • Civilianize enforcement -you know it makes sense.
    • http://www.cstodd.co.uk
Re: British Standards in relation to Emergency Lighting.
« Reply #2 on: September 26, 2010, 07:19:55 PM »
Thomas,

You call up the recommendations of part1 plus the requirements of parts 7 and 8 if you want to be strictly correct.
Colin Todd, C S Todd & Associates

Offline Tom Sutton

  • Hero Member
  • *****
  • Posts: 2287
Re: British Standards in relation to Emergency Lighting.
« Reply #3 on: September 26, 2010, 07:56:55 PM »
Thanks to both of you
GFSM
Stating 1999 version was a mistake I used the 2005 copy.

Colin
That is what I eventually did but it does seem more complicated then it needs too. One document would be much easier with no repetition. 

All my responses only apply to England and Wales and they are an overview of the subject, hopefully it will point you in the right direction and always treat with caution.