It falls on the designer to ensure that measures are in place to reduce false alarms. Personally, unless delays are built in such as with the alarm sense detectors or the hush facility arrangement by C-tec or indeed an analogue addressable system is employed then I fail to see that the arrangement is compliant.
Mixed systems have disadvantages which have been largely overcome by the systems noted above and are probably just as easy to install, if not more so!.
To be honest, I see the sort of system to which you refer on a regular basis. No body seems to give a toss as long as the paperwork is available. I am dealing with a very similar situation at this very moment. As part of a Licensing Scheme requirement, I detailed my concerns regarding the likelihood of false alarms in one installation on an Inspection Report and sent it to the Enforcing Authority some time ago. Seems at the time they just regarded it as a Certificate. Following several false alarms, tenants complained, solicitor involved and of course the big stick is out for any one remotely concerned with the system! The system was only about 10months old when I inspected it. Contractor, whoever he was, did not issue certification!
Regards,
Lyle Dunn