"Most fire detection and fire alarm systems in dwellings comprise smoke alarms, which are usually fitted in,
at least, the circulation areas, such as hallways and landings. BS 5446-1:2000 requires that the sound
output of a smoke alarm be at least 85 dB(A) at three metres. Most domestic doors attenuate sound by
around 20 dB; greater attenuation can occur in the case of solid doors, such as fire doors. It is therefore
unlikely that a smoke alarm on, for example, the upstairs landing of a two-storey house will produce a sound
level of 75 dB(A) at the bedhead in each bedroom, particularly if the bedroom doors are shut; levels of 55
dB(A) to 65 dB(A) are more likely. There appears to be no evidence to show that lives are being lost due to
inadequate audibility of the fire alarm signal from smoke alarms, except where people are incapacitated to
such a degree that even much higher sound levels would not waken them".
The quote above is from BS5839-6 2004. The Standard is for dwellings and the comment may be justified. The problem is that the same Standard is often used in HMOs. Althought it does acknowledge the minimum 75dbA at the bedhead recommended in 5839-1 2002 it introduces ambiguity where I believe none should be.
My daughter moved in to an HMO (ordinary 2-storey dwelling with 3 separate bedrooms). Incredibly it did not have smoke detectors fitted. Apparently the HMO Licence Scheme hadnt reached that far at the time! Any way the Landlord was quick to respond to my intervention. A LD3 Grade D system was fitted and certification issued by the diligent contractor. A quick inspection by Daddy smoothed some furrows. However, as always I frowned upon the prudence of relying on a single smoke detector fitted in the landing outside the 3 bedrooms. Sound pressure levels were 63dbA at the bedhead. A couple of months later, all the doors in the property were changed as the Licence system eventually extended its reach to that part of the city. Well of course, the inevitable attenuation caused by the new doors has resulted in sound levels being reduced to 44dbA in one bedroom! The Authority controlling the Licence are happy as they have the recently issued Fire Alarm Certificate and all the remedial fire safety work required by them has been carried out.
I do not know who the made the comments in BS5839-6 quoted above or on what statistical information he or she was assessing the risk but fire safety takes on a different hue when your own daughter is involved. The limited cover offered by a LD3 Grade D system may satisfy the lily-livered approach taken in normal dwellings but do we really have to suffer a disaster before we insist that ALL bedrooms in HMOs should be fitted with both detector and sounder!
Regards,
Lyle Dunn