Author Topic: Carbon Monoxide alarms  (Read 6888 times)

jakespop

  • Guest
Carbon Monoxide alarms
« on: May 27, 2011, 10:31:05 AM »
When recommending Part 1 and part 6 systems, are there combined CO and Smoke alarms available and recommended? A recent case locally has raised concern especially in bed sits and similar.

Offline AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2480
    • http://www.firewizard.co.uk
Re: Carbon Monoxide alarms
« Reply #1 on: May 27, 2011, 08:46:03 PM »
Kidde have produced dual smoke/CO alarms for a while, but the one's I last saw were single station battery only ones, no dual supply or link facility.
Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36

Offline colin todd

  • Hero Member
  • *****
  • Posts: 3473
  • Civilianize enforcement -you know it makes sense.
    • http://www.cstodd.co.uk
Re: Carbon Monoxide alarms
« Reply #2 on: May 28, 2011, 12:24:01 AM »
You can get co/smoke multi sensors
Colin Todd, C S Todd & Associates

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Carbon Monoxide alarms
« Reply #3 on: May 28, 2011, 09:36:53 AM »
I may have misread the original posting but I took the posting to be about the potential for combining both life safety detection of CO and detection of fire within a single detector. I think we will all agree that multi sensor heads as part of a fire alarm and detection system should only be used for the detection of fire.

Are the parameters for a CO (life Safety) detector the same as those for a  CO (combustion gas) fire detector? I was under the impression that the alarm thresholds for each purpose were  very different but would be pleased to be corrected.

The life span of a life safety CO detector is generally a maximum of 7 years according to most manufacturers. The typical life span of a smoke fire detector is 10 years.

If the two purposes  were combined in a single head presumably the whole thing would need to be replaced at 7 years, which if part of a large system could be a significant cost burden. It would also need to give a very differnt alarm signal to differentiate between the two purposes.

Although programmable, I believe the default for most systems with multi sensor heads would be to give just a pre alarm in the presence of CO only. Sorry if I have gone off at a tangent and the only reason for the OP was the control of unwanted signals.

« Last Edit: May 28, 2011, 11:37:06 AM by kurnal »

jakespop

  • Guest
Re: Carbon Monoxide alarms
« Reply #4 on: May 28, 2011, 12:45:28 PM »
Thanks Kurnal. Yes the original posting was enquiring about possibility of combining in one detector. It seems more satisfactory to have a single stand alone CO detector as well as smoke/heat detectors from what you say and which is what I suspected. Thanks.

Offline SamFIRT

  • Sr. Member
  • ****
  • Posts: 382
  • Looking for the truth
Re: Carbon Monoxide alarms
« Reply #5 on: May 29, 2011, 08:37:31 AM »
As a matter of interest what are the threshold limits for activation of a life risk CO detector as opposed to CO detectors used to raise awareness of fire? Anyone know?
Sam

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Carbon Monoxide alarms
« Reply #6 on: May 29, 2011, 04:19:32 PM »
From what I can glean on the web,

The European Standard for carbon monoxide alarms  EN50291
 
Main alarm requirements:
 
1- at 30ppm CO, the alarm must not activate for at least 120 minutes
2- at 50ppm CO, the alarm must not activate before 60 minutes but must activate before 90 minutes
3- at 100ppm CO, the alarm must not activate before 10 minutes but must activate before 40 minutes
4- at 300ppm CO, the alarm must activate within 3 minutes


Whereas a typical CO fire detector alerts at 40ppm. Source http://www.tycoemea.com/english/pdf/datasht/fire/PSF094A.pdf
 


Midland Retty

  • Guest
Re: Carbon Monoxide alarms
« Reply #7 on: May 31, 2011, 04:12:21 PM »
As many have already said combined CO/Smoke detectors are available on the market, and have been for a while.

Their sole purpose is to detect fire, they are not designed to warn of possible carbon monxide poisoning.

A Carbon Monoxide (Fire) detector should not be mixed up with a Carbon Monoxide Alarm (which alerts people to carbon monide poisoning)

Offline AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2480
    • http://www.firewizard.co.uk
Re: Carbon Monoxide alarms
« Reply #8 on: May 31, 2011, 11:50:16 PM »
Yes, I agree they are different beasts - however I misread the original question and thought it related not to CO fire detectors, but CO life safety detectors.

The Kidde unit I referred to is a domestic use device that has an ion smoke chamber for fire and a CO detector for life safety against CO poisoning from gas appliances in the one unit and uses voice alarms as well as different tones to identify the different warnings
Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36

Offline Gel

  • Full Member
  • ***
  • Posts: 101
Re: Carbon Monoxide alarms
« Reply #9 on: October 16, 2011, 02:10:49 PM »
For info this product type can gain UL Approval for a combined smoke & CO alarm, but
in UK there is a conflict with IP ratings so that one combi alarm cannot achieve BS Kitemarking
to the smoke EN 14604 and CO EN 50291 Standards.

There has been a frustration on this for some years, but there may be some movement in short term to
remove the IP rating from battery CO alarms; in US they also have hard wired variants too.

In a fire situation, the alarm will always give priority to the danger of fire; Kidde's has advantage
of being only UK one where there is a voice warning so resident totally clear as to what danger has
set off alarm.
Some FRS have used these for boat safety initiatives.