"To my mind there should be no gap, if i can see through the other side then smoke can get through. The reason i ask is that we have double doors where this is the case."
ahmedh - stick with this! You're right to say if you can see through the meeting gap then you haven't got smoke sealing. Things have moved forward quite well since the halcyon days when I was involved in such things, but I believe companies like Lorient and Sealmaster have done a lot of work, and they should be able to provide you with good advice.
Don't get hooked up on having the smoke seal in one edge and intumescent only in the opposite one. There are all manner of ways of achieving sealing at the meeting edges, from one combined seal in one edge, through fire seal in one edge with a smoke seal in the other, to a mix of fire and smoke seals in each edge, but making sure the fire seals don't sit opposite each other.