Author Topic: Override facilities on Exit Doors- Nursing Care  (Read 6122 times)

jakespop

  • Guest
Override facilities on Exit Doors- Nursing Care
« on: March 13, 2011, 06:28:08 PM »
I am assessing an old Nursing Home which has recently been upgraded and refurbished to provide a mental health facility. Final exits are linked to fire alarm and release upon actuation and on power failure. No override facilities fitted. As long as it is regularly tested to ensure correct operation, would override facilities be required?

Offline Phoenix

  • Hero Member
  • *****
  • Posts: 677
  • Get a bicycle. You will not live to regret it
    • MetaSolutions (Fire Safety Engineering) Ltd.
Re: Override facilities on Exit Doors- Nursing Care
« Reply #1 on: March 13, 2011, 08:43:39 PM »
Yes.

But I have another query...

I've just bought a new pair of trousers and, frankly, I was a little pessimistic in my judgement of my equitorial circumference.  I wear these trousers with a belt and also, to be on the safe side, a pair of braces.  As long as I check my belt and braces regularly do I also need to tie a bit of string around my waist?

Offline CivvyFSO

  • Hero Member
  • *****
  • Posts: 1583
Re: Override facilities on Exit Doors- Nursing Care
« Reply #2 on: March 14, 2011, 12:09:33 PM »
Yes. Because the actual potential impact of your pants falling down, thus displaying your unmentionables, is an unacceptable risk. However unlikely, the actual severity is the controlling factor.

Midland Retty

  • Guest
Re: Override facilities on Exit Doors- Nursing Care
« Reply #3 on: March 14, 2011, 12:24:25 PM »
The answer is "it depends"

It depends on where the care home is located within the country. You will find brigades do have differing policy on over ride devices.

It might appear obvious why over-rides weren't provided in this scenario, however some would argue that there are ways and means to provide over-ride devices which are either inaccessible or not obvious to the patients / service users.

Others (including myself) argue that so long as regular testing is carried out you can dispense with over ride devices in certain environments.

My advice is don't second guess - ask the local fire service about their policy on over rides. Im not saying that their policy will be reasonable, but you will atleast know where you stand, and from that you will better positioned to counter, prevent or justify the lack of over rides.

It will save your client a lot of ball ache in future especially the next time an inspector calls.

Offline SandDancer

  • Newbie
  • *
  • Posts: 29
Re: Override facilities on Exit Doors- Nursing Care
« Reply #4 on: March 14, 2011, 03:49:35 PM »
I have a similar new build with these devices fitted, Fire Service ok with it and I am happy from a Fire point of view, but raises big security issues if you lose power to building in an none alarm situation. This might cause you problems in the future :(

Offline colin todd

  • Hero Member
  • *****
  • Posts: 3473
  • Civilianize enforcement -you know it makes sense.
    • http://www.cstodd.co.uk
Re: Override facilities on Exit Doors- Nursing Care
« Reply #5 on: March 14, 2011, 09:35:01 PM »
Duh! You can provide back up on the power supply to the security devices.
Colin Todd, C S Todd & Associates

Offline AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2490
    • http://www.firewizard.co.uk
Re: Override facilities on Exit Doors- Nursing Care
« Reply #6 on: March 14, 2011, 11:55:31 PM »
Yes, in fact it is not uncommon for each mag-lock to have a PSU and battery cabinet provided so that a power fail will keep it working.
Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36

Offline SandDancer

  • Newbie
  • *
  • Posts: 29
Re: Override facilities on Exit Doors- Nursing Care
« Reply #7 on: March 15, 2011, 08:47:34 AM »
Colin, I was only pointing out something you need to check on, the doors fitted on the site I mentioned above don't have battery back up, whether it was an oversight or due to cost a dont know, but it is something which Jakespop might want to check and advise his customer on.
AntonyB, appreciate the technical details, I will admit when it comes to all things electrical I ask the right questions, but leave the specifics to the experts ;D

jakespop

  • Guest
Re: Override facilities on Exit Doors- Nursing Care
« Reply #8 on: March 15, 2011, 11:41:12 AM »
Just to clarify. If a battery cabinet is provided the door will still work normally. So in event of fire alarm, the door should release. If there is a problem with relay could this not prevent door releasing automatically,hence the need for manual override?