Replies from various fire alarm engineers regarding BS5839 compliance, etc:
"Offhand, it won't comply with 27.2 :
4) at the point at which the power supply(ies) to any radio-linked component can maintain the
component in normal operation for no more than seven days, and, in addition, in the case of fire alarm
devices, 30 min in the alarm condition, a fault warning should be given at the control and indicating
equipment;
If the mains linked smoke lost the mains supply and battery backup, I doubt you would get a fault at the panel."
"No head removal notification either. You can can pull those things down and just leave the base and no-one would now.
I wouldn't think that would comply when using a panel capable of monitoring head removal.
Plus the mains could fail inside the flat rendering that detector to run from its battery and again no indication at the panel.
All very ropey and unnecessary if you ask me.
All in all though a good example of trying anything to avoid a re-wire. Sparky job was it?"
"I suppose for the part 6 element it may only have to be local to the flat but I can't get my head around the whole bringing it back to an enclosure/radio base thing."
It doesn't comply if the coverage is needed for life safety due to structural deviations from code. If it was code compliant and didn't need a system at all it doesn't really matter, but would give a false sense of security due to it's various areas of fault that would not be readily apparent.