If the Fire Risk Assessment determines that this is the appropriate solution then let no man put it asunder.
What are the alternatives after all? There are two.
1- Appoint a fire alarm responsible person 24/7 to be on standby in case someone burns the toast in their flat.
2- Train all occupiers on how to silence and reset the panel. I have found that with such systems they do get a lot of experience at it.
With many addressable systems and multi sensor heads now available the Cause and Effects can be modelled to emulate domestic smoke alarms whilst the heat element contributes to L3 protection of the communal areas, but this still creates the problem of someone having to reset the panel every time they burn the toast, because BS5839-1 requires a manual reset.
Rafiki tried to overcome this with their SITA 200 panel which had a self reset function after 5 minutes if the smoke has cleared. The trouble was that its non compliant with BS5839 -1 and the medicine is as bad as the ailment because whilst the system will reset itself after 5 minutes if the smoke has cleared it cannot do so more quickly. 5 minutes seems an eternity in such circumstances.