This is the sort of training for use of powder on class C fires:
http://www.youtube.com/watch?v=EX_8ii-ygJEWhat the BS seems to be saying between the lines is that you shouldn't provide cover for class C risks in normal environments and to follow what 99% of non specialist extinguisher training courses and material say for gas fires which is to shut off the supply* or leave it to the fire brigade.
So most buildings don't need powder in boiler rooms and the like, whereas if you own a LPG cylinder distribution business you may need to consider advanced training, and hose reels as well as powder extinguishers.
In practice where there is a current Powder extinguisher because an area has a Class C risk in a normal non specialist environment we are advising they are changed for CO2 as we don't want staff tackling the gas fire and it is not feasible/risk appropriate to provide the specialist hands on training for a gas fire.
So boiler rooms, gas valve rooms, areas using small amounts of LPG and similar don't need powder any more (in my opinion).
* which means there is no longer a Class C fire so you don't need powder.