A hospital has just been found to have IT cabling installed without any fire stopping! This has been going on for some time which is pretty worrying to say the least.
IT cables that pass through compartments/sub-compartments should obviously be fire stopped. My question is what type of fire stopping material should be used?
looking ad ADB and the 'Red Book' it mentions 'proprietry seals'.... can someone tell me what is the difference between proprietry seals and intumescent mastic
I would imagine that a ball park figure would be mastic is ok for say penetrations of up to 100mm x 100mm but anything more than that should have an appropriate cavity barrier.
Also what is the opinion of the forum of third party accrediation such as FIRAS?
Also, also

... unless I'm reading it wrong the mastic etc itself does not have BS number ...it is the finished fire stopped partition that should be made good to it's original BS 476 Part 20...is this right?