Apologies if I have missed the obvious but I can not see anything which states that service penetrations within riser shafts should not be fire stopped (it is clear from the guidance that any doors to the shafts should be 30 minutes fire rated). Typically I would presume that it is implicit that fire stopping is not needed provided that the access points to the shaft are 30 minutes fire rated (and there being no reference to compartmenting riser shafts on all floors). However, as mentioned in my link to a previous thread in my original message, the use of fire stopping between the floors within protected riser shafts is widespread.
I also note from one of the case studies in the purpose built flats guide a reference to 'provide a good standard of fire stopping to any openings around cables and pipes in common areas above fire doors and within service riser cupboards' (A13.4).
Furthermore, Lacors states that services should be 'enclosed within fire- resisting construction AND fire stopped' (19.7).