Author Topic: BS 9251:2005(Rev)  (Read 7125 times)

Offline gor810

  • Newbie
  • *
  • Posts: 14
BS 9251:2005(Rev)
« on: January 09, 2016, 12:04:08 AM »
Hi all and Happy New year

I have a question which I need some guidance on please.

Is there any requirement for an automatic suppression system installed in accordance with the recommendations contained in BS 9251 to be linked in to the fire warning and detection system main fire alarm panel installed within a residential care premises.

Some information on the premises. The premises are equipped throughout with a category L1 FA system. The sprinkler system has been installed within a newly added wing to the building so as to comply with Building Regulations. The sprinkler system has not been installed by way of a compensatory feature. Standards of fire resistance of doors, walls and ceilings and the rest are those expected of a residential care premises.

I would welcome any comments.



Offline Jim Scott

  • Jr. Member
  • **
  • Posts: 60
Re: BS 9251:2005(Rev)
« Reply #1 on: January 09, 2016, 10:09:45 AM »
The 2014 edition of 9251 does recommended it.

However, it does also say that if the premises is provided with a comprehensive fire detection and alarm system, it may not be necessary.

If the premises is fitted with an L1 system, I would suggest that you will have an alarm activation prior to any sprinkler head activation anyway.

Offline gor810

  • Newbie
  • *
  • Posts: 14
Re: BS 9251:2005(Rev)
« Reply #2 on: January 09, 2016, 12:07:14 PM »
Thanks for the information Jim. I don't have the 2014 amended document yet and was not aware that it was recommended.

I agree that smoke detectors would operate before the sprinkler heads in the part of the premises to which I refer and raise the alarm throughout the premises.

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: BS 9251:2005(Rev)
« Reply #3 on: January 09, 2016, 12:14:24 PM »
And gives the benefit of a confirmation at the fire alarm panel to the staff that something signi ficant is happening (and escalating ) with alerts from the sprinklers supplementing the detection system. Usually the sprinkler panel is remote from the fire alarm panel and investigation of this alarm in isolation may place extra demands on staff and delay the the investigation of the fire alarm. 

Offline gor810

  • Newbie
  • *
  • Posts: 14
Re: BS 9251:2005(Rev)
« Reply #4 on: January 09, 2016, 02:18:41 PM »
Yes. Thanks for that input Kurnal.

Offline colin todd

  • Hero Member
  • *****
  • Posts: 3473
  • Civilianize enforcement -you know it makes sense.
    • http://www.cstodd.co.uk
Re: BS 9251:2005(Rev)
« Reply #5 on: January 10, 2016, 03:22:01 PM »
It probably only costs two and sixpence to do, and is a useful bonus.
Colin Todd, C S Todd & Associates

Offline Tom Sutton

  • Hero Member
  • *****
  • Posts: 2287
Re: BS 9251:2005(Rev)
« Reply #6 on: January 11, 2016, 09:19:19 AM »
gor810 Have you received a messages from me.
All my responses only apply to England and Wales and they are an overview of the subject, hopefully it will point you in the right direction and always treat with caution.

Offline Mike Buckley

  • Hero Member
  • *****
  • Posts: 1045
Re: BS 9251:2005(Rev)
« Reply #7 on: January 11, 2016, 09:20:45 AM »
The other side of the issue is that if the sprinkler system is linked to the alarm panel then the staff will get a warning that the sprinkler system has gone off which may occur without there being a fire. This will probaly not be due to a fault in the sprinkler system but I deal with a hotel chain all of whose hotels are srpinkered and every hotel has a tale of the sprinkler heads being set off by people using them as coat hangers, people accidentally knocking them, convenient poitne to hang Xmas decorations etc.
The presence of those seeking the truth is infinitely to be preferred to those who think they've found it.

Offline gor810

  • Newbie
  • *
  • Posts: 14
Re: BS 9251:2005(Rev)
« Reply #8 on: January 12, 2016, 03:00:35 PM »
Thankyou very much to everyone for their inputs on this matter. This has been most helpful to me.

Offline gor810

  • Newbie
  • *
  • Posts: 14
Re: BS 9251:2005(Rev)
« Reply #9 on: January 14, 2016, 06:38:26 PM »
Thankyou very much Tom Sutton for the information. Appreciated.