New build, small block of flats, single staircase condition (grd, 1st & 2nd floors), Three flats per floor, all have inner protected hallways with FD30(s) flat entrance doors which are accessed directly from each staircase landing i.e there are no lobbies. TD is irrelevant with no lobbies but would vary, with one floor within 4.5 metres and another exceeds but would be under 7.5. The building fits Approved Document B Section 2.21 for "small premises".
Whats the forums opinion should the staircase be lobbied or not.
My view is it should, at all levels including the top floor.
As there are more then two flats per floor Diagram 9b is ruled out, leaving Dia 9a to apply.
Further reference is made to lobbies in Approved Document at Section 4.34 (a) and states that lobbies can be excluded in small premises as defined at 4.6(a) then to 3.33 (3.32), however the way I see it small premises in section 3.33 (3.23) is for buildings "other then flats" (flats having their own definition of small premises at section 2.21).
Am I reading it correctly or is anyone aware of a hidden paragraph in the Approved Document that says doors between the top of the stairs and the dwelling entrances can be omitted in such a building.