It's virtually all been said above, e.g. Golden, but here's my thoughts. The increase in pressure in the upper part of the fire room can be quite high (several hundred Pascals have been recorded in some cases), and this is particularly significant if a ceiling jet is moving hot gases towards the door. The over-pressures will tend to take advantage of any gaps around the top of the door. (This is an important point - We know that doors do develop faults and gaps over time.) The over-pressures will not generally fully transfer into the lobby so any gaps around the lobby-to-stairs door will not have smoke and hot gases forced through to the extent that the first door will. A single door, whether 30mins or 60 mins, reduces significantly the additional protection to the stairs that is otherwise given by the lobby.
This has varying importance in different buildings. It's a more important consideration in a single staircase hotel than it is in a multi-staired office block. But remember that people with impaired mobility might take a considerable time to descend the stairs in a taller building, whatever its use, so the protection to the stairs should not be skimped on.
As for discounting whole staircases where lobbies aren't provided, I think that this can be over the top but, at the moment, I don't have an alternative to suggest.