Author Topic: Travel distance 999 style  (Read 4589 times)

Offline lyledunn

  • Hero Member
  • *****
  • Posts: 503
Travel distance 999 style
« on: March 04, 2020, 06:25:47 PM »
Travel distance for a C2 risk profile in one direction according to Table 15 in 9999 is 9m. At the bottom of the same table it says; ?The two-way travel distance limit for hotels is measured from the entrance to the bedroom/suite, not from the most remote part of the bedroom/suite?.
Thus the implication is that one way travel should not be measured from the entrance door of the bedroom. That would be almost impossible to achieve and I do believe a mistake has been made in 9999 in that regard. It would seem to me that an allocation of 9m in the bedroom and 9m in the protected corridor would be appropriate. Now if we put sprinklers in, then we move down one risk profile to C1 which allows 13m in one direction. Would you read this as 13m in the bedroom and 13m in the protected corridor?

Offline lyledunn

  • Hero Member
  • *****
  • Posts: 503
Re: Travel distance 999 style
« Reply #1 on: March 07, 2020, 08:11:31 PM »
Another Saturday night and I ain?t got nobody!! It?s Cat!

Offline Revol

  • Jr. Member
  • **
  • Posts: 71
Re: Travel distance 999 style
« Reply #2 on: March 19, 2020, 10:57:13 AM »
Table 15 of BS 9999 says 13 meters for the maximum TD in single direction with additional fire safety measures? ?