BB100 and door closing devices
« on: April 07, 2007, 07:48:46 AM »
Heres a quote from BB100

Door closing devices should not have an opening moment in excess of the
following values unless the doors are held open on electro-magnetic hold-open
devices:
infants and juniors ≤ [10] years and disabled - (36) Nm
pupils ≥ [10] years - (47) Nm

Anyone know where they are coming from on this one with the magetic hold open device?

If a child cannot be expected to open a door under normal conditions is it not likely to impede escape in a fire when the magnet has released?

Offline jokar

  • Hero Member
  • *****
  • Posts: 1472
BB100 and door closing devices
« Reply #1 on: April 07, 2007, 06:43:30 PM »
Is it not likely that under normal operating conditions, children will open doors on there own whilst under evacuation conditions there will be a staff member with them leading the way out and the train of children will keep the door open.  Values are obviously set from part M but vcan not be set as a generic as each set of circumstances will differ.