Author Topic: Smoke detection in flats  (Read 3764 times)

Offline nigelB

  • Newbie
  • *
  • Posts: 7
Smoke detection in flats
« on: September 13, 2007, 06:47:55 PM »
My brother in law is the management agent for a block of flats. 4 floors, 4 flats on each floor and a common staircase serves  the building. The fire authority enforcement officer has told him he requires automatic smoke detection throughout.  I thought he only needed 30 min fire doors and battery operated smoke detector in each flat.  can someone confirm this please

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Smoke detection in flats
« Reply #1 on: September 13, 2007, 07:07:18 PM »
Depends on the construction of the building,- if all floors and walls  are 1 hour fire resisting, if all flats have a protected entrance hall, if all flats have a half hour door to the entrance, if travel distance across the landing to each flat is no more than 4.5m and theres no other fire risk in the staircase then  mains powered smoke alarms in each flat to LD3 spec of BS5839 part 6 would suffice and no common alarm in the staircase.
The 4.5m could increase to 7.5m if there is  ventilation in the stair
But if these conditions are not met its essentially classed as a HMO and the fire service may then rightly require more than this under the RRO and it may be subject to licensing under the housing act.
Take a look at Approved document B available for free download - google for planning portal.

Offline nigelB

  • Newbie
  • *
  • Posts: 7
Smoke detection in flats
« Reply #2 on: September 13, 2007, 07:49:39 PM »
Thank you kurnal