O.K just had another instance of a status panel setting the FD&A system off. Electrical test and inspection was being undertaken within a concert hall, swimming pool, ice rink. The company undertaking the test & inspection isolate the incomming supply to one of 36 DB's to enable safe means of working. The Fire Alarm activates, the fire service are summoned via an ARC due to the fact that site security could not confirm a false alarm call, all they knew was the alarm had gone off saying sprinkler interface. After a ninety second staff alarm the building was evacuated via the P.A.V.A. When everthing had settled the site maintenance staff could not confim whether this had happened before (and as maintenance staff do "this has not happened before, I think") we were call in to investigate. The cables from the sprinkler room were traced half way across the building to a status panel located within a security room. The Fire Alarm interface was connected to a set of relay contacts within this panel. The Fire Alarm interface monitored for open and short circuit via the required E.O.L and fire resistor, but this was defeated by the status panel. This was pointed out to the maintenance staff and the fact that for the past 17 years this was the case. The next question was Solution.