A historic mill of 4 floors, top storey height 20m, has brick walls, brick floors on cast iron columns and beams and was erected in 1906. It has rising wet mains in each stair. The rising main is directly connected to the towns mains and the gauge standing pressure is 50psi- ie 3.3Bar at ground floor. No facilities for fire service to supplement the supply. I assume it will be 1.3 Bar at top floor level and neither use nor ornament for fire fightng.
Article 38 requires the maintenance of such facilities if they have been provided under the requirements of Building Regulations or any other enactment.
Does anybody know if these mains would have been originally provided under an enactment ( Mill is in Oldham and is used as a warehouse)?
I take the view that if the main was installed as an insurance company requirement rather than a legal requirement it may be legally removed. The insurers are not interested either way.
I am trying to persuade the owner to convert it to a dry riser but they are reluctant to do anything unless there is a legal requirement. No significant changes have been made to the building in recent times that would enable application of approved document B5.