Hi Guys
Thanks for your replies.
But going back to the hotel scenario - what if a fault were to occur overnight to the fire alarm system, lets say an arsonist disables the fire alarm system at a panel in a hotel annexe and then starts a fire. As aconsequence it fails to detect a fire which has started somewhere and as a result residents are put at serious risk or worse.
Owing to the fact it is a hotel,is it reasonable to expect that alarm system be monitored 24/7 or is once a day enough? again what if a fault occured which diabled the fire alarm system?
Could you argue to a magistrate that checking the panel once every 24 hours is sufficient?.
You wil probably find that the panel is lockable, usually. There will be windows on the cover to enable you to monitor its status.
If you check the panel daily and a fault indicator is not indicating such then that should be sufficient.
Thats really all you can be expected to do daily. A fault can develope at any second, but you can't be expected to employ anyone to sit and stare at the panel 24/7.
Are you doing a RA or enquiring as the hotel manager?