Thanks for the feedback kurnal, you never cease to amaze me with your absolute extraordinary knowledge of fire safety matters, hygroscopic is a new word in my vocabulary now.
What I have been finding out in my discussions with manufactures of intumescent products for upgrading existing panelled doors so far is that their products need different thicknesses of door panels to be effective once applied, and strict following of their application instructions to provide a 30 minute integrity, so far I have been told this ranges from 6mm to 12mm thick panels, they can provide me with test evidence, and confirmation that their products comply with the tests contained in BS 476 -22 ( thats what i am being told)
I have also been told by one that a 1mm intumescent paper, veneer or panel, once activated, expands to twenty times its original size, but the panel must be at least 6mm thick to begin with to achieve 30 minutes.
I have managed to get my hands on the book by ASDMA you suggested, I never knew there was so much that could be written about doors.