Author Topic: External Stairwells....confused??  (Read 2114 times)

Offline brearabbit

  • Newbie
  • *
  • Posts: 1
External Stairwells....confused??
« on: August 08, 2008, 11:08:19 AM »
Morning all,

I have recently been told that the external stairwell to our building (iron type one painted black) has to be assessed every 3 years by a structural engineer.  According to the report I had done 'the external stairwell or any other external structure used as a means of escape has to be inspected by a structural engineer every 3 years'?  

I am interested to know where the requirement for this comes from??  Is it statutury??  Can anyone help.

Thanks,

Steve

Offline wee brian

  • Administrator
  • Hero Member
  • *****
  • Posts: 2424
External Stairwells....confused??
« Reply #1 on: August 08, 2008, 11:25:31 AM »
Not laid down in any particular regs - you have duties to ensure safety and maintenance of escape routes under fire safety and general health and safety law.

The 3 years comes (from memory) in the recomendations of a British Standard. They suggest it gets a regular once over as they can get rusty and unsafe.

If you think 3 years is over the top then you need to be able to evidence why you are doing something different from normal practice.