Step below Velux Escape Window
« on: July 29, 2008, 06:05:33 PM »
Can anyone tell me if it is possible to put a fixed step in floor level below a velux escape window if the height from ffl to bottom opening part of the window is slightly more than 1100mm? (The height is 1245mm so I thought maybe a 145mm high step below the window?)

Thanks!

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Step below Velux Escape Window
« Reply #1 on: July 29, 2008, 06:48:59 PM »
There is absolutely no reason why not- it must be a  permanent fixture. However some local authority building inspectors dont seem to like them- sometimes they turn such proposals down saying thay there is no guarantee that it will not be removed in future.

Presumably this is from the first floor because escape windows are no longer acceptable from most loft conversions according to the 2006 ADB

Offline mhairig

  • Newbie
  • *
  • Posts: 3
Step below Velux Escape Window
« Reply #2 on: July 29, 2008, 07:09:09 PM »
Hi, yes it's from the first floor of a 2 storey building albeit the velux is in the roof plane (the insulation line is at rafter level). Guess I will need to double check with BC then! Thanks for speedy response.

Chris Houston

  • Guest
Step below Velux Escape Window
« Reply #3 on: July 29, 2008, 07:18:53 PM »
Seems odd to refuse to accept a safety feature on the basis that it might be removed in future.  The same argument could be used to refuse to accept any safety feature (fire doors, fire alarms, sprinklers).

Offline Psuedonym

  • Sr. Member
  • ****
  • Posts: 315
Step below Velux Escape Window
« Reply #4 on: July 29, 2008, 08:34:17 PM »
I know someone who just spent £35K on an extension with 3 velux windows in. The adhesive which sticks the guarentee is still on the glass :rolleyes:
Ansul R102 Kitchen Suppression Enthusiast


Created using refurbished electrons to ensure I do my bit to save the planet...Polar bear cubs saved so far:2.75. Reduced due to effects of Carbon Footprint on the carpet. It's a bugger to shift...

Chris Houston

  • Guest
Step below Velux Escape Window
« Reply #5 on: July 29, 2008, 09:03:34 PM »
I don't understand your point.

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Step below Velux Escape Window
« Reply #6 on: July 30, 2008, 12:35:16 PM »
Quote from: Chris Houston
I don't understand your point.
Chris, he's developed a new type of glue and is trying to promote it.

Pseudonym, is he the one who invented the glue that B&Q use to stick the labels onto their finished timber and are a real bugger to get off?
We're not Brazil we're Northern Ireland.

Offline Fishy

  • Hero Member
  • *****
  • Posts: 777
Step below Velux Escape Window
« Reply #7 on: July 30, 2008, 02:19:48 PM »
I'm 99% sure that there has been one or more determinations regarding this very subject - have a look at the last few year's worth (can get at them via the CLG website).

Offline mhairig

  • Newbie
  • *
  • Posts: 3
Step below Velux Escape Window
« Reply #8 on: July 30, 2008, 05:14:23 PM »
CLG website - what is this please?!

Chris Houston

  • Guest

Offline Psuedonym

  • Sr. Member
  • ****
  • Posts: 315
Step below Velux Escape Window
« Reply #10 on: August 03, 2008, 10:00:33 PM »
Quote from: nearlythere
Quote from: Chris Houston
I don't understand your point.
Chris, he's developed a new type of glue and is trying to promote it.

Pseudonym, is he the one who invented the glue that B&Q use to stick the labels onto their finished timber and are a real bugger to get off?
Precisely NearlyThere! That glue is a real bugger!!
Ansul R102 Kitchen Suppression Enthusiast


Created using refurbished electrons to ensure I do my bit to save the planet...Polar bear cubs saved so far:2.75. Reduced due to effects of Carbon Footprint on the carpet. It's a bugger to shift...