What you need to think about with the lobby is it's actual purpose. It is there to keep smoke out of the stair to ensure that the stair is always passable, so if you can acheive that by other means then you have cracked it. AFD does nothing to keep smoke out of the stair, the only choices you have are a positive pressure stair, or if you can have negative pressure in the accomodation area adjoining the stair. (This second option if very rarely used, and the positive pressure system is quite expensive) The only real benefit for you of using a positive pressure system is more useable/lettable floorpsace. Over a buildings lifetime the extra rental on the space may pay for the system. An engineered solution utilising a pressurised stair may be there to warrant the removal of other staircases, and as such would be a great saving on floorspace.