What prevent of designing and manufacturing a conventional fire alarm system with loop circuits rather than radial circuits, no EOL any more.
Would that be a good addition to the old limited technology (as it still beneficial to some small applications) or this would be just like running backward?
Thank you
Benz,you would give a paracetemol a headache sometimes!!!I can see the benefit of having a ring circuit as opposed to a radial for a conventional system with regards to keeping the system "fed" from both ends,but it falls down on a couple of points (at least).
Firstly,unlike an addressable system,there would be difficulty tracing an open circuit because you couldn't get a print out to show where in the loop the break was (ie - between device 30 and 31 say).
Secondly,because a zone is restricted to 2000m2 then a conventional zone circuit can only cover this area.On the cost side you are increasing the cabling required per zone which is a major factor - weighing up the cost of conventional/addressable equipment over cable costs then the difference in the cost of detectors on a flat 2000m2 ceiling would be around £300/£400 between conventional and addressable per zone.
The two-wire systems offer the benefit of an addressable system (sounders and interfaces on the same circuit as the detection) but keep the installation costs down by using a radial circuit.