Author Topic: Hoses for CO2 extinguishers  (Read 3662 times)

Offline kewellman2000

  • Newbie
  • *
  • Posts: 3
Hoses for CO2 extinguishers
« on: May 09, 2009, 09:33:39 AM »
Can anyone please give me guidance on the above in terms of
1/ Frequency of inspection
2/ Frequency of re-test
3/ Frequency of replacement
4/ Which standard refers to the above info is it an EN standard or a BS

Thanks

Offline Thomas Brookes

  • Sr. Member
  • ****
  • Posts: 290
Re: Hoses for CO2 extinguishers
« Reply #1 on: May 10, 2009, 07:34:54 PM »
Hoses?

Do you mean Horn's
I refuse to have a battle of wittts with an unarmed person.

Offline kewellman2000

  • Newbie
  • *
  • Posts: 3
Re: Hoses for CO2 extinguishers
« Reply #2 on: May 11, 2009, 08:51:11 AM »
No I do mean the hoses not horns.

Any ideas ?

Cheers

Offline AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2480
    • http://www.firewizard.co.uk
Re: Hoses for CO2 extinguishers
« Reply #3 on: May 11, 2009, 11:40:14 AM »
BS 5306-3 covers the maintenance of portable fire extinguishers, including their components, which would include the horn & elbow and horn & hose of CO2 extinguishers.

The user monthly check would usually identify any obvious damage and the basic service each year would involve a thorough inspection for wear & tear, damage and functionality, including renewal of O-rings &/or fibre washers to ensure a good seal of the hose/elbow to the valve.

Any obvious damage would result in replacement - air entrainment through a cracked horn can affect extinguishing capability and a totally broken off horn and elbow presents an injury damage risk as with the resulting loss of pressure reduction the extinguisher once discharged can literally fly off like a rocket and has caused serious injury and fatalities. A worn hose could rupture affecting efficacy as well as being a hazard.

During the 10 year overhaul it is normal (but not mandatory)to renew the horn & hose/horn & elbow assemblies.

(A revised edition of this standard is due for release imminently)

BS EN 3 details the functional requirements for hoses and horns fitted to CO2 extinguishers
Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36