The only Rafiki i have commissioned i got the pleasure of getting the manual thrown at me by the sparky.
he had done his job-run all the cables on top of the suspended ceiling. used nylon ties throughout. not set up any sound levels or detector types. Guessed the spacings.
etc etc
according to him all i had to do was "blow smoke into everything"
The commissioning engineer always runs the risk of upsetting the system designer or system installer. It can also lead to a loss of future business.
This is because the general term 'commissioning' has a defintion of 'putting into operation' to most people whereas the BS term includes much more.
An offer of a Fire alarm commissioning service to BS should clearly include a description of what it includes (this will also go someway to explain the 'high' cost) and specifically that deviations (I used that word purposely so it isn't confused with variations) from BS will be included on the certificate and explained in such a way that the commissioning purchaser realises the implications of those deviations being recorded.
The question I ask is should a 'businessman' also offer a service that basically involves just 'blowing smoke into everything' if that is only what the customer wants? (as long as the customer clearly realises that this is not a BS commissioning)