Author Topic: Fire System design regarding roof lights  (Read 3428 times)

Offline Big_Fella

  • Full Member
  • ***
  • Posts: 232
Fire System design regarding roof lights
« on: February 17, 2009, 01:16:00 PM »
I have a scenario where an L1 system is being proposed for a school, which is fine.

The school is split on two levels, where one end of the school goes up full height of the building i.e. the corridor is 7 metres high, and has glazed roof lights in the roof of this corridor providing natural light.  The roof lights are 2.5 m2 and are approx 2 metres in depth.

Is there a requirement to provide automatic detection within the roof lights or will detection on the underside ceiling suffice?

Many thanks in advance.
« Last Edit: February 17, 2009, 02:58:56 PM by Big_Fella »
** Knowledge is power, I'm still working on both **

Graeme

  • Guest
Re: Fire System design regarding roof lights
« Reply #1 on: February 17, 2009, 05:25:43 PM »
to the standard any rooflight over 800mm in depth.

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Re: Fire System design regarding roof lights
« Reply #2 on: February 17, 2009, 05:39:58 PM »
As Graeme says, detection is required in 'lantern lights' over 800mm in depth but also in any lantern light (less than 800mm in depth) also used for ventilation.

Offline Big_Fella

  • Full Member
  • ***
  • Posts: 232
Re: Fire System design regarding roof lights
« Reply #3 on: February 17, 2009, 08:12:24 PM »
Thanks guys. Good definitive answer. I shall apply this.

** Knowledge is power, I'm still working on both **