The following is an extract from HTM 05-02
5.42 A hospital street should:
a. be constructed to the same fire-resisting standards as a fire compartment;
b. have a minimum clear width of 3 m;
c. be divided into a minimum of three sub compartments, each with a maximum
length of 30 m;
d. at ground floor – have a minimum of two final exits located:
(i) at every extremity of the hospital street;
(ii) so that the maximum travel distance between final exits is no more than
180 m measured along the length of Hospital Street;
(iii) so that the maximum distance from a compartment exit to a final exit is no
more than 90 m;
e. at upper levels – have access to a minimum of two stairways each in separate
sub compartments, which are located so that:
(i) the maximum distance between stairways does not exceed 60 m;
(ii) the maximum single direction of travel within the street does not exceed 15 m;
(iii) the distance from a compartment exit to a stairway is no more than 30 m;
f. contain no other accommodation except sanitary accommodation.
Hope thats of use to you