In answer to your questions, it appears that the guidance you refer to is only mentioning those doors that have some sort of access control, and it could therefore be argued that doors that are for emergency use only etc. are not covered. I'm sure this document means to cover all types of such door locking, but the way it is written, it seems to preclude some types.
The guidance is asking for an Emergency Door Release switch that meets the same design standards as the type of switch used as a manual call point in a fire alarm system. Type A means there is only a single action to operate it; for example it doesn't include a hinged cover. The guidance is also alluding to the requirement of the locking device being fail-safe and also releasing automatically on operation of the fire alarm. One of the fail-safe requirements is due to 'system error' but it doesn't describe what 'system error' actually means.
BS7273-4 covers all doors with electric locking devices, includes the same switch type requirements, fail-safe operation but also includes much more detail and more recommendations than the document you refer to. Interestingly, BS7273-4 doesn't cover the circumstances of any 'if' and 'when' recommendations in respect of interfacing the door release system to a fire alarm system but just how you should do it when you do do it. An earlier question on this forum asked why there was a link to the fire alarm when an EDR was anyway required. This was a good question and no-one could point to any authorative guidance recommending this. However the document you refer to includes it as a recommendation.
I think this is another fine example of this country's love of producing many versions of similar guidance recommendations. Every man and his dog seems to want to get in on the act.
You would think that they would all try to 'sing from the same hymnsheet' but, as always, we end up with a cacophony of undechipherable noise!
I could understand it if the building regs just mentioned complying with BS7273-4 or gave an exact precise summary of the recommendations of BS7273-4 but, instead, we end up with something that is similar but not actually the same.
There are too many cooks stirring the broth, as normal.