Hi guys,
I am currently undertaking a FRA on a small purpose built block of flats. Aged 1990s.
Compartmentation is not thought to be an issue, as not that old and appears to be to a good standard where seen.
However the layout or design does not appear to conform to CP3, BS5588-1 or most version of AD B.
We have ground, 1st, 2nd, 3rd and 4th. Single stair building. Not small single stair building as one floor too many! However, the 4th floor must be at 11m or under, this is obviously helps.
3 flats per floor accessed from a lobby. Travel distances are very small, easily within 4.5m. AOV provided to head of stair.
No ventilation to lobby outside flats.
After considering guidance, it appears that the landlord may need to provide ventilation to the lobby. However the lobby is not on an external facade, therefore no space for a shaft.
There is currently no fire alarm for the communal areas, I know it is not needed, I know evry argument there is against detection, as it can be more trouble in residential.
However, due to the lack of ventilation, would LD3 communal area detection compensate?
Or, does anyone think it should be ok as it is, considering travel is small and AOV at head of stair and the top floor is wihtin 11m from ground?
Stinky.